Hello:

Will have to come up with a new topic other than on MOV's, but it is certainly interesting.
Funny, you think you understand something, a bit, and then realize how you really don't.

Anyway -

As I mentioned in my previous post, will be putting in a "secondary" wired-in surge protector (an Intermatic AG 2401 IND )
to try and protect a new furnace circuit board that is apparently susceptible
to lightning induced transients. It fried during last lightning storm.

Eventually, the electrical service box will be replaced with a new one. When it is, will install a whole-house variety. But for now, will have to settle for the point-of-use, wired in variety.

There is the typical on/off AC power furnace switch located in an EMT tubing run, about a foot or so from the furnace proper. This seems like a good place to wire it in, and install it.

Have been thinking about whether it makes more sense to wire it in on the upstream side of the switch, or whether it should be placed on the downstream side (the end closer to the furnace) ?

Seems to me that it probably doesn't matter at all, but thought I'd ask.

Any thoughts on ?

Thanks,
Bob

Tools for Electricians:
Re: Best Location For Surge Protector ? #129772
08/17/05 02:44 PM
08/17/05 02:44 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
I would wire it on the load-side, just so it has a disconnect.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Best Location For Surge Protector ? #129773
08/17/05 03:12 PM
08/17/05 03:12 PM
D
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
I am curious about the Emt feeding the furnace, does it have a wire just sleeved in it or does the Emt go all the way back to the panel?

If it is sleeved, what type of wire is in it?


Dnk.......

Re: Best Location For Surge Protector ? #129774
08/17/05 04:02 PM
08/17/05 04:02 PM
P
Paulusgnome  Offline
Member
Joined: Jun 2004
Posts: 56
Christchurch, New Zealand
For best results, install the surge suppressor as physically and electrically close to the item being protected as possible.

I would not install it in the same panel as the switchgear because when a suppressor cops a big enough surge it sometimes blows to bits in order to save the equipment being protected.

A separate enclosure installed adjacent to the switchboard is probably best.


Mark aka Paulus
Re: Best Location For Surge Protector ? #129775
08/17/05 04:32 PM
08/17/05 04:32 PM
R
Robert11  Offline OP
Member
Joined: Aug 2005
Posts: 10
Boston, MA
To Dnkldorf:

Hello:

Will let you know once I open it up; probably in a week or two.

Thanks for help,
Bob


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,487 Are you busy
188,678 Re: Forum
178,379 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9687 MB (Peak: 1.1059 MB) Zlib enabled. Server Time: 2018-11-16 01:16:38 UTC