Magnetic forces on non-braced cables #129609 05/23/05 11:29 PM
Joined: May 2005
Posts: 1
M
mustangwilly Offline OP
Junior Member
How can I calculate the forces on non-braced cables during a fault? The cables are freestanding and rub against several undesireable places. I am concerned the insulation will be compromised, the screening exposed and thus generate additional spectaculor results. It is a 5KV cable.

Tools for Electricians:
Re: Magnetic forces on non-braced cables #129610 05/26/05 07:17 AM
Joined: Sep 2003
Posts: 649
W
winnie Offline
Member
I don't know the equations that apply for determining the force over time in faulted three phase circuits.

The DC equation is pretty simple, this equation also applies for the 'instantaneous' force between two conductors at a given moment in time if the current is changing (note): the force between two current carrying conductors is proportional to the current in one times the current in the other, and inversely proportional to the distance between them. (note: this is only strictly true for changing currents if you ignore the speed of light [Linked Image] )

See http://hyperphysics.phy-astr.gsu.edu/hbase/magnetic/wirfor.html for the equation and a calculator.

After you've calculated the force between the conductors, you will also need to consider the geometry of the situation. Even if the conductor forces are not all that high per unit length, it may be that the force on a length of cable creates a concentrated load at a single point on the cable where it hits a support.

-Jon


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,034 Are you busy
205,039 Re: Forum
193,154 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3