open circuited ct's #129361 02/01/05 01:31 PM
Joined: Jan 2005
Posts: 2
D
DJT Offline OP
Junior Member
Hello everyone,
I would appreciate a detailed theoretical explanation of why a meter/relay class CT develops such a high open circuited voltage. Aside from the ammount of iron, what other deciding factors determine the voltage level?

Dave

Tools for Electricians:
Re: open circuited ct's #129362 02/01/05 01:52 PM
Joined: Jul 2002
Posts: 8,337
Trumpy Offline
Member
If the load is removed from a Current Transformer secondary winding, while there is still current flowing in the Primary winding, the secondary EMF will rise to a high and very dangerous level, this is an attempt to maintain the secondary current in the winding.
Factors that contribute to the magnitude of this voltage would include, the Primary current flowing, the turns ratio between Primary and secondary and the impedance of the secondary winding.
Hope this helps.

Re: open circuited ct's #129363 02/02/05 05:05 PM
Joined: Dec 2004
Posts: 16
T
Tinkerer Offline
Member
The CT is designed to cause a current in the secondary in proportion to the current in the primary. If there is a current in the primary the secondary tries to increase the voltage to force the current through the infinite resistance presented by the open circuit. remember v=i*r so when the r is infinite and the current is finite the the voltage will be infinit.

Re: open circuited ct's #129364 02/02/05 05:05 PM
Joined: Jan 2005
Posts: 354
P
pdh Offline
Member
Think of the CT as a step-UP transformer ... because that is what it actually is (stepping current down means stepping voltage up). The difference is that the primary (the conductor going through the window) is "wired" in series with another load (the entire metered load). You have a low number of turns on the primary (usually 1) and a high number of turns on the secondary (for a 600:5 that would be 120 turns). Actual voltage calculation depends on a lot of factors, and under load will drop low. But the turns ratio can determine what you could get in an open circuit condition.

A transformer reflects the impedance of the secondary back upon the primary at the given ratio. That's why a normal transformer primary will draw more or less current depending on the impedance connected to the secondary. As you reflect more impedance back against the current flow going through the CT window, the voltage drop at the window increases. It won't be infinite since it's not perfect coupling, so you can't stop the current in the conductor with an open CT. Potentially (no pun here ... this is lethal) you can get the supply voltage (how hard it will try to make sure the load current flows through the window) times the turns ratio of the CT.

Don't mess with live CT's unless you are specifically trained in the procedure.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,787 Are you busy
205,000 Re: Forum
193,115 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3