open delta banking concerns #129332 01/21/05 09:50 PM
Joined: Jan 2005
Posts: 6
S
splitzapper Offline OP
Junior Member
hello there..friends please help me with my problem.
Is it possible to bank 2 transformers in open delta if it has different kva rating?
assuming that both have the same voltage rating,impedance ratio and frequency.
If it is possible, then how would i compute the power contribution of each transformer?
your inputs would truly be appreciated.
thanks in advance,.,.


Oh Yeah!
Tools for Electricians:
Re: open delta banking concerns #129333 01/22/05 12:01 AM
Joined: Jan 2005
Posts: 19
P
peterpang Offline
Member
My answer to your question is yes!
As I know there are 7 condictions should be met when you parallel 2 transformers:

1)P-S voltage must be the same!
2)Proper polarities connetion
3)Percentage impedence of one is between 92.5% and 107.5% of the other
4)Same tap setting
5)Identical phase displacements.
6)Identical frequency
7)Equivalent impedence and X/R ratio

So I think it is possible to bank 2 transformers in open delta even if they have different kva ratings!!!
And the total Apparent Power=(P1+P2)x86.6%!

Re: open delta banking concerns #129334 01/22/05 12:30 AM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
The utilities do this all the time. You might have a 50 kva and a 10 kva banked together. This is done when the 3 phase load is small. The 3 phase load is 57% on each transformer and the lighting transformer(50kva) will carry 100% of the single phase load.

[This message has been edited by Bob (edited 01-21-2005).]

Re: open delta banking concerns #129335 01/22/05 02:09 AM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
 
There are some assorted cut-and-paste notes from El Paso Electric on non-symmetrical delta- and open-delta-secondary transformer banks. [It is unnecessary that the pair of transformers be matched.] These configurations are mostly intentionally unsymmetrical to allow for inherently unbalanced 1ø and 3ø loads.

Save file http://6L6.net/bjarn/ecn.DSOexcerpt-7delta.pdf ~1.1MB {available for a short time}

Another [fee-based] reference is §8 in ANSI/IEEE Std C57.105-1978 …Application of Transformer Connections in Three-Phase Distribution Systems.




[This message has been edited by Bjarney (edited 01-22-2005).]

Re: open delta banking concerns #129336 01/22/05 03:10 AM
Joined: Jan 2005
Posts: 6
S
splitzapper Offline OP
Junior Member
guys thanks a lot. now it is clearer to me.i hope you would still answer mr questions cause i have a lot. btw i am a newly licensed practitioner so your inputs would truly help me...once again thanks..


Oh Yeah!
Re: open delta banking concerns #129337 03/06/05 12:40 PM
Joined: Mar 2005
Posts: 1
M
marcel1444 Offline
Junior Member
The seven requirements are important when paralleling transformers.This is when the transformers primarys are connected together and their secondaries feed the same load. When you are banking transformers
like three transformers feeding a three phase load or two transformers in an open delta configuration the impeedance is not important. The only exception is primary delta and secondary delta. Then you want to have your impeedances close. In the case of the open delta with the 50kva and the 10 kva you woutd be just fine. If you bank a transformer with two others the one with the lower impedance will take more of the load. Being that the impedance of the 50kva is most likely lower than the 10 kva you are in good shape.


marcel1444

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
BigB 4
NORCAL 3
Popular Topics(Views)
270,143 Are you busy
204,502 Re: Forum
192,681 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3