Motor Hook 12 lead #129287 01/03/05 03:25 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
We have a 12 lead mtr. For a fire pump . Voltages on name plate 200/400.
We're being told it can be hooked up to a Straight 208 vOLT 3 PHASE. One Starter/
Wiring diagram on mtr shows Start y Run Delta.
20 hp. anyone ever run into this???

Tools for Electricians:
Re: Motor Hook 12 lead #129288 01/03/05 05:09 PM
Joined: May 2004
Posts: 186
A
aland Offline
Member
Could it be a two speed motor? sounds to me like a set of windings for low speed and a set for high speed simple resistance test across windings might give you a clue!

Re: Motor Hook 12 lead #129289 01/03/05 05:21 PM
A
Anonymous
Unregistered
Just use a start Y, run Delta starter. and feed it with the 208 Y.

The starter will have two contact sets and coils which should be interlocked.

Re: Motor Hook 12 lead #129290 01/03/05 05:27 PM
A
Anonymous
Unregistered
http://www.usmotors.com/products/ProFacts/1-105ystart.htm

Sorry I could not edit my original post. Hope this helps. 12 leads because your 200/400.

Re: Motor Hook 12 lead #129291 01/03/05 07:01 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
The run configuration is delta, so hook it up per the low voltage run connection.
Don


Don(resqcapt19)
Re: Motor Hook 12 lead #129292 01/03/05 11:40 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
 
From a liability standpoint for building-fire protection, it may be a serious mistake not to have specific documentation that the starting method called out by the pump manufacturer is unambiguously provided but the fire-pump controller, with the two correctly interconnected.

If the fire pump is intended for reduced-voltage starting, a controller providing only full-voltage starting may be a critical misapplication.

Re: Motor Hook 12 lead #129293 01/07/05 09:53 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Answer is Delta Run. Checked with several motor rewind shops ect.

Its also in Electrical Engineering Pocket handbook.
Thanks guys for the imput. Never to old to learn. Yoopers
L1=1-6-7-12
L2=2-4-8-10
L3=3-5-9-11

low voltage run

Re: Motor Hook 12 lead #129294 01/08/05 01:06 AM
Joined: Nov 2004
Posts: 3
E
electricpete Offline
Junior Member
"If the fire pump is intended for reduced-voltage starting, a controller providing only full-voltage starting may be a critical misapplication."

Reduced voltage starting protects the power system, not the motor. Prevents things like neighbor's lights flickering. Would not afffect the fire pump function.

[This message has been edited by electricpete (edited 01-08-2005).]

Re: Motor Hook 12 lead #129295 01/08/05 03:03 AM
Joined: Oct 2000
Posts: 2,721
Scott35 Offline
Broom Pusher and
Member
electricpete,

1st off, welcome to ECN!

I believe the point of which Bjarney is referring to
(reply covering the Wye / Delta starting intentions of the Motor and the possible liability involved with misapplication),
would be critical issue to the design and application of this particular Motor/Pump assembledge.

In other words, if the connected Pump has something similar to excessive head pressure (per an Air Compressor's Pump at start without "dumping" the pressurized air between cylinder and tank), the Motor may either stall / continuous Locked Rotor scenario, or draw excessive Current for an excessive time period - both of which will cause one or both of the following:
<OL TYPE=A>

[*] Overcurrent device trip,

[*] Huge volumes of Smoke loss from Motor's windings.
</OL>

I can see the Lower Voltage (Wye Connection) starting means allowing the Pump to get things flowing enough to allow full speed / line voltage connection of Motor to enable without the effects of "A" and/or "B" above.

***DISCLAIMER***
I am probably wrong about the starting intentions, along with Bjarney's reply, so feel free to flame away at me if above information is indeed bunk!

Just my 2¢

Scott35

edited to fix bad HTML tagging ... Bad tag!!! go sit in the corner!!!

[This message has been edited by Scott35 (edited 01-08-2005).]


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Motor Hook 12 lead #129296 01/14/05 08:13 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Controller & motor supplied by the Fire Pump installers , Reason I had asked the question was for my piece of mind.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,256 Are you busy
206,143 Re: Forum
194,135 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3