Been doing elec work for around 30 years and still not clear on why the neutral and ground are bonded together at the main service in a home, but a subpanel has to have the neutral and ground isolated.


The Golden Rule - "The man with the gold makes the rule"
Horizontal Ad
Joined: Mar 2001
Posts: 333
S
Member
If the neutral/grounded conductor and EGC are bonded together at a subpanel, the neutral's current flow back to the main panel will be partially carried on the EGC. This would be a potential shock hazard for someone coming in contact with the EGC.

steve


Steve
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
But it seems that if they are tied together at the main panel, it would act the same at the sub panel too.
And wouldn't there be a EGC potential shock hazard at the main panel too?


The Golden Rule - "The man with the gold makes the rule"
Joined: Mar 2001
Posts: 333
S
Member
Only if the neutral opened up or at least didn't have a good connection with the source.


Steve
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
But if the neutral opened up at the sub-panel, it is still tied together to the ground at the main panel.


The Golden Rule - "The man with the gold makes the rule"
Joined: Mar 2001
Posts: 333
S
Member
But with no N-EGC connection at the sub, there won't be current flow on the EGC. Current is always trying to get back to the source(transformer, generator). With the neutral open at the sub panel, the return current is now on the ungrounded conductors, with this causing erratic voltages on the sub panel's circuits.


Steve
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
But why would there be current flow on the SP EGC when it is tied to the neutral at the main panel.


The Golden Rule - "The man with the gold makes the rule"
Horizontal Ad
Joined: Sep 2003
Posts: 650
W
Member
Basic electrical theory: Electric current flows in _circuits_. When the equipment ground is bonded to the neutral at a single point only, there is no closed path, and thus no circuit. With no closed circuit, current cannot flow.

This ideal of single point grounding is only achieved when there is a single customer on the transformer. With multiple services connected to the same transformer, you have multiple point grounding of the electrical system, and thus closed circuits on the grounding electrodes and grounding electrode conductors, with current flowing through these parallel ground circuits. Plumbers have been shocked cutting water pipes after the neutral connection has failed.

-Jon

Joined: Apr 2002
Posts: 2,527
B
Moderator
 
Find a new or used copy of IAEI/Soares’ Book on Grounding.

Joined: Dec 2004
Posts: 1
P
Junior Member
Well I am taking a deep breath and making a first post in reply to this. Take it easy on me this is my understanding of grounding.

1. grounding rod and netural. you never want to be able to get a shock from netural. So by grounding them at service entrance, all neturals throughout the system stay as close to netural as possible.

2. purpose of a ground wire is safty not "normal" operation, so you never want current in a ground wire under normal conditions. This begs the question, how would you get current in a ground wire? Hot wire shorts to something grounded. this creats a total short and will blow the breaker. Yes netural is at the same potential, but you do want current flowing in the netural.

3. ground loops. these are caused by current flowing in the ground wires. Your ground is no longer a true ground. You could get shocked by touching "grounded" metal. Main cause of these is netural and ground connected somewhere it should not be.

Well, at least this is my understanding of it.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Top Posters(30 Days)
BigB 6
timmp 2
Popular Topics(Views)
329,665 Are you busy
254,502 Re: Forum
237,005 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5