ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Lowes Selling this fan
by timmp - 07/25/21 10:58 PM
How's all our Non-US folks doing?
by djk - 07/23/21 09:13 PM
Switched Receptacles -Top or Bottom?
by donles - 07/23/21 10:51 AM
Do You Travel?
by Bill Addiss - 07/20/21 04:26 PM
Backup Generator Done Right
by timmp - 07/18/21 12:20 PM
New in the Gallery:
February, North East Indiana
February, North East Indiana
by timmp, July 25
Red Green would be proud
Red Green would be proud
by timmp, July 25
Who's Online Now
0 members (), 42 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#128974 06/09/04 09:37 AM
Joined: Dec 2001
Posts: 201
A
ayrton Offline OP
Member
Why do you think the code prohibits running parallel conductors smaller than 1/0??

#128975 06/09/04 12:00 PM
Joined: Jan 2002
Posts: 59
C
Member
If you study the ampacity tables you will see that in the larger sizes of wire an increase in size results in relatively little increase in ampacity. Forinstance, a 50% increase from 10 kcmil to 10.5 kcmil results in an increase in carrying capacity in amperes of less than 15%.
There is no need to parallel conductors smaller than 1/0 because the difference between the carrying capacity in these sizes is much less pronounced.
Although the NEC places the limit, it is really physics that limits paralleled conductors to 1/0 and larger.
Creighton


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 69
Joined: January 2002
Top Posters(30 Days)
timmp 7
Rachel 4
Popular Topics(Views)
281,471 Are you busy
215,106 Re: Forum
201,971 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5