solid state flame control and generator #128895 03/14/04 03:46 PM
Joined: Mar 2004
Posts: 6
R
randyagr Offline OP
Junior Member
Been having trouble running a household furnace with a solid state flame control on standby generator power. The furnace runs flawlessly on the grid, but on standby, the flame keeps droping out, and after three tries at ignition, locks out. The generator is a 30 year old 3 phase wye 15kw. The furnace is 120v single phase. I have checked the voltage at the control, it is perfect, even under startup surge. Any ideas?

Tools for Electricians:
Re: solid state flame control and generator #128896 03/27/04 07:34 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
How clean is the power at the control module? Do you have access to an oscilloscope to look at the waveform?

Some electronics can be very sensitive to noise, spikes, or a distorted waveform, any of which your generator may be producing. In the case of high frequency noise, an appropriate bypass capacitor across the power input may help.

Re: solid state flame control and generator #128897 05/02/04 08:01 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
The neutral from the generator must be properly grounded and the polarity at the furnace must be correct.

Tim

Re: solid state flame control and generator #128898 07/17/04 08:08 AM
Joined: Mar 2004
Posts: 6
R
randyagr Offline OP
Junior Member
Thanks for your help. I know the polarity is correct. There are 2 ground rods plus an underground copper gas line between the generator and the furnace. What do you guys think about running the control circuit with a pure sine wave inverter? If I use magnetic contactors hooked to the control board to run the furnace motors and ignitor, i can get down to about 2 amps, thus reducing the size (and expense) of the needed inverter.

Re: solid state flame control and generator #128899 07/17/04 01:31 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Quote
What do you guys think about running the control circuit with a pure sine wave inverter?
I don't like it because I think that if it runs off the normal supply it should run off the generator. If the supply is correct polarity at the furnace, it makes me wonder about the grounding. Is your generator neutral bonded to the ground system? If it is, I'm out of ideas.

Re: solid state flame control and generator #128900 07/17/04 02:15 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
It could be an interaction between the genset voltage regulator and the AC-powered electronic assembly. A power-rated oscilloscope to look at line-voltage waveforms may be the next step.

Re: solid state flame control and generator #128901 07/17/04 04:13 PM
Joined: Mar 2004
Posts: 6
R
randyagr Offline OP
Junior Member
ok, the genset is hooked up using a 8-4 rubber covered cord. (it is a manual hookup, not an auto start). there is a ground rod at the box. (it is located in a outbuilding) I do not have a separate one wire ground for the genset. I could try running another ground wire. Also, my house has a ground rod for the service entrance. Could you explain what you mean by an interaction between the voltage reg and the ac powered elec assy? I can tell you i understand how these contol boards sense flame. Also, if the generator output is not a pure sine wave, then what?

Re: solid state flame control and generator #128902 07/18/04 05:27 AM
Joined: May 2004
Posts: 7
F
Frank Martino Offline
New Member
Due to mechanical inertias of the generator and voltage regulation that is less than the regulation of the utility grid, I suspect that voltage sags from the generator are causing the flame sensors to fail to see the flame.

See:

Sag Correction for Small Equipment Without Using UPS Systems

"The most common power quality problem encountered is that of voltage sag. All equipment is susceptible to dropping off line if the incoming voltage is low enough for a long enough period of time.

"Publications found in the trade journals give the following generalized typical equipment shut-down characteristics...

"* Boilers with flame sensors may indicate a loss of flame with voltage sags, thus causing needless shutdowns."
http://www.powerqualityanddrives.com/sag_correction_without_ups/

Frank

Re: solid state flame control and generator #128903 07/18/04 11:55 AM
Joined: Mar 2004
Posts: 6
R
randyagr Offline OP
Junior Member
ok, thanks for the reply. It could be a voltage problem. I have watched the voltage at the control as the furnace cycles with a digital voltage meter. I honestly can not see the voltage drop below about 118 and that is during the blower startup surge. Do you think the voltage is sagging faster than can be seen on the digital meter? If it does, will a Ferroresonant transformer change fast enough to solve the problem? The burner will light and burn for maybe 30 seconds, then drop out and relight. thanks for any thoughts you might have.

Re: solid state flame control and generator #128904 07/23/04 01:20 AM
Joined: Jul 2003
Posts: 394
B
Big Jim Offline
Member
You could spend a lot of time and energy searching and installing solutions or you could go to the local computer store and buy a UPS for under a hundred bucks.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,897 Are you busy
205,757 Re: Forum
193,867 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3