20
22
Can anyone suggest how the scott35 excel spreadsheet for single phase 120/240 could be modified to correctly calculate the load for a 120/208 panel? Also unsure of the use of abbreviations on the following columns: LTG, REC, MSC, BKR, LCL, BUS. Final question, would say a single phase compressor running at 208v and 24.4 amps be listed under columns A and B on the same row or on successive rows in order for the spreadsheet to correctly tabulate amperage? Thanx in advance ![[Linked Image]](https://www.electrical-contractor.net/ubb/redface.gif) ) cb btw: this post is also under general discussion, sorry for the repetition. cb
So that we're on the same page, answers here refer to '1ph3.xls' in Psched1.exe.
Looks like LTG - lighting, REC – receptacle, MSC - miscellaneous, BKR – breaker (size), CKT – circuit number (odd-left/even-right), BUS – Aø or Bø bus connection.
The summed per-phase loads should work for a 120/208V 3w bus and ø-n or ø-ø connected loads, but they do not cancel [worst case] in the feeder ‘neutral’ lead like that of 120/240V 3w circuits. {Has nothing to do with harmonics, BTW.} If, for example, there were two 120V 16A loads connected Aø-N and Bø-N then the feeder neutral would also see [worst case] 16 amperes. A 208V 24A load connected Aø-Bø would reflect no neutral current. {duh.}
Although Scott’s schedules apply to most panelboards and switchboards, be aware that 1- or 2-pole molded-case breakers in "I-line" boards don’t fit the usual bussing-sequence rules.
Scott35, you have provided E-C.net members with a very worthwhile set of spreadsheets, that can be modified to fit specific needs. You have done the hard part…thanks!
[This message has been edited by Bjarney (edited 08-17-2002).]
Broom Pusher and Member
Bjarney, Thanks for the kind words!!! You covered the answers correctly, plus the other related items! I really want to build a better mouse trap ![[Linked Image]](https://www.electrical-contractor.net/ubb/wink.gif) for the Panel Schedules. When I get them finished and Debugged, I'll add them to ECN. CAB, I posted a reply to this in the General Discussion area, so feel free to view that message if needed. Scott S.E.T.
P.S. To contact me via E-Mail, use this address: dtbigred@pacbell.netScott S.E.T.
Shinnston, WV USA