Voltage drop calculation #127800
01/04/02 09:44 AM
01/04/02 09:44 AM
C
cinkerf  Offline OP
Member
Joined: Dec 2000
Posts: 84
Pittsburgh, Pennsysvania. ...
In today's code question of day http://www.ecmag.com/cqd/index.cfm?ID=20020104 two methods for performing voltage drop calculations were given for an A.C. circuit. Is one method better than other? Is one method more popular than the other?

Tools for Electricians:
Re: Voltage drop calculation #127801
01/04/02 09:57 AM
01/04/02 09:57 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,902
NY, USA
Frank,

I've always tried to use formulas that are simple (for me) to remember. In this case Ohm's Law; (I = E/R)

E = I x R where E is the Voltage

Bill

Re: Voltage drop calculation #127802
01/04/02 11:18 AM
01/04/02 11:18 AM
F
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Thanks Bill. By the way, Happy New Year....

Re: Voltage drop calculation #127803
01/04/02 11:21 AM
01/04/02 11:21 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
For short distances (less than 150 ft), I use simple formulas. I like the Square D Motor Data Calculator voltage drop feature.

For longer distances I like to consider the impedance of the system rather than only the resistance. This means worrying about the raceway, Power Factor, and phase configuration. I use the tables in the Ferraz-Shawmut Book of Electrical Information.

Re: Voltage drop calculation #127804
01/04/02 02:09 PM
01/04/02 02:09 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I just found this site with some downloadable elecrical software. It has a series voltage drop calculator for multiple loads on long runs. It is free and I downloaded it this morning. Looks like it will work nice, but I haven't really played with it yet. http://www.edreference.com/default.asp
Don(resqcapt19)


Don(resqcapt19)
Re: Voltage drop calculation #127805
01/04/02 06:16 PM
01/04/02 06:16 PM
F
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Over the years I've take several certification examinations. Only small calculators were permitted to be used. I've had luck using the following calculation for voltage drop for single phase circuits: VD=2KLI/CM. x.866 if three phase circuit. For these particular exam questions power factor, raceway etc were not a factor. I was thankful for that...

For those of you who took exams, what formula did you use?

[This message has been edited by Frank Cinker (edited 01-06-2002).]

Re: Voltage drop calculation #127806
01/09/02 07:49 AM
01/09/02 07:49 AM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Guys,
Ugly's has always been the standard around here. Don, Uglys was issued to me by the IBEW in my apprenticeship, since we came through about the same time didn't you use it ? If they quit publishing Uglys I've always said I'm leaving the trade. It is also the standard used locally for most every test.

Single phase, 2 wire = 2K X L X I / Cm

3 phase, 3 wire = 1.73K X L X I/ Cm

K = 12.9 for copper, 21.2 for aluminum
L = length, I = amps, and Cm = Circular mil area from Chap 9, Table 8

The only thing you have to check occasionally is the "K" rating, that has moved around since I came in the trade because the cma table was revised.

I've been around long enough that #10 wire was 10,000 cm, it has been revised to 10,380, but the formula has pretty much remained the same. [Linked Image]

Re: Voltage drop calculation #127807
01/10/02 11:33 PM
01/10/02 11:33 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
George,
They didn't give us "Ulglys", but those are the formulas that we were taught.
Don


Don(resqcapt19)
Re: Voltage drop calculation #127808
01/11/02 03:41 AM
01/11/02 03:41 AM
E
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
The K factor has changed through the years because the Ohms per 1000ft figure in Table 8 of Ch 9 depends on the assumed temperature. In the '87 code they stopped assuming 25C and started assuming 75C.
K is just shorthand for: (dc resistance value) X (circular mil area) divided by 1000.
You have to watch out for the assumed temperature if you are going to use the formula with a K factor...not to be confused with K factors of transformers!

[This message has been edited by Elzappr (edited 01-11-2002).]

Re: Voltage drop calculation #127809
01/12/02 12:48 AM
01/12/02 12:48 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
I would not have passed my journeyman's without an UGLY's... Is the 2002 out yet?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 