ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Old POCO Letter
Old POCO Letter

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 38 guests, and 34 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#127791 01/02/02 09:31 AM
Joined: Jan 2002
Posts: 2
A
Junior Member
Question regarding ampacities for cable. 1999 NEC Table 310-16 basically reflects ampacities of current carrying conductors in raceways, CABLE, etc. Then there Table 400-5 discussing ampacities of cords and CABLE.

Q1: For a #8 AWG conductor, there are differences in ampacities between the two Tables. With no regard to ambient temperature etc. T. 400-5 lists certain types (SJO, STO etc.), while 310-16 lists conductor insulation types (RHW, THW etc.) Given this circumstance, are there two types of "CABLE" available that fall each respectable NEC table?

(I do know there is the new 2002 code but for our writings we only current copyright for 99 code)

Any assistance in this matter would be greatly appreciated.

AF Electrician
Course Developer

Horizontal Ad
#127792 01/02/02 09:39 AM
Joined: Oct 2000
Posts: 2,749
Member
See Section 240-3. Protection of Conductors
Conductors, other than flexible cords and fixture wires, shall be protected against overcurrent in accordance with their ampacities as specified in Section 310-15, unless otherwise permitted or required in (a) through (g).


Joe Tedesco, NEC Consultant
#127793 01/02/02 10:26 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Yes, there are two types of cables.

First are the flexible cord style (i.e. extension cords) these are protected according to NEC99 400-5.
Second are all of the other styles (i.e. NM, and AC) which are protected according to NEC99 310-15.

#127794 01/02/02 10:50 AM
Joined: Jan 2002
Posts: 2
A
Junior Member
Now that clears things up and makes sense! Thanks!


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
337,984 Are you busy
263,139 Re: Forum
243,476 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5