An existing aerial feeder consists of 800 feet of 6AWG and 100 feet of 10AWG. It's 120 volts, single phase. 15amp. load. What is the proper method of determining voltage drop when there are two different size conductors on the same feeder.
I use VD=2KLI/CM

Horizontal Ad
#12606 08/13/02 05:07 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Use the formula the caculate 800 ft of #6 with 15 amps. Do the same for the #10 at 100 ft with 15 amps and add the two together for the total VD.

#12607 08/13/02 05:14 PM
Joined: Aug 2001
Posts: 7,520
P
Member
I'll second that.

Quote

VD=2KLI/CM

Huh??? [Linked Image]

#12608 08/14/02 05:17 AM
Joined: Jul 2001
Posts: 311
F
Member
pauluk-

VD= Voltage drop
2= length of circuit x "2"
K= K-factor. 12.9 for copper conductor
L= Length of circuit
I= Amps
CM= Circular mill

#12609 08/14/02 06:54 AM
Joined: Aug 2001
Posts: 7,520
P
Member
Thanks. It was getting late and the CM part just didn't register in my mind for some reason (we don't measure in circular mils here).


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Top Posters(30 Days)
Popular Topics(Views)
558,682 Are you busy
432,958 Re: Forum
401,960 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5