#124621 11/12/06 11:18 AM
Trumpy Offline OP
Photos and info submitted by Shockme77:
I'm just about done trimming-out a house and I thought
I'd share some pics of the work I've done. I've never before sent in pictures for the discussion forum and I understand that I'm opening myself up to criticism, so fire-away!. This single-family dwelling is in Scotch
Plains, New Jersey and hasn't been sold yet. Just
slightly less than 5k SQ', and the asking price is $1.4.
#124622 11/12/06 11:46 AM
Doesn't look like the builder cared enough to option out the place with a structured wiring system cabinet. Also doesn't look like enough branch circuits.
I think I would have used some of the KO's in the TJIs to run my home runs through.
#124623 11/12/06 12:00 PM
Your AHJ lets you bundle that many Romex together for long runs without derating?
#124624 11/12/06 01:33 PM
Violation.
Check Section 334.15(C)
Otherwise it would pass inspection.
Alan--
One solution would be to drop the wires, install 1X2 or other running boards, and put the wires back up. You should check with the manufacturer of the T joist since they do not like to have things nailed or screwed to the bottom edge.
A--
[This message has been edited by Alan Nadon (edited 11-12-2006).]
Alan--
#124625 11/12/06 01:44 PM
It's only a bundle if you fail to "maintain spacing." The plastic trees he used to support the romex do maintain spacing between the wires. Indeed, it looks like he exceeded code requirements for support.
Since he's using proper hangers, I'm not sure what the use of running boards would accomplish; there does not appear to be any significant 'droop' to the cables. Perhaps this will need to be addressed in the next code cycle?
The KO's in the joists NEVE line up. Nor would using them for support -in lieu of runing boards- support the cables any better than they already are supported.
Awfully nice that the gutter crew saw fit to go around the service drop; usuallym they try to pry it out from the wall!
The only 'nit' I see to pick at is the lack of working space in front of one of the air conditioner disconnects.
#124626 11/12/06 04:57 PM
Where is the outlet for the air conditioning condensors?
Do you have a ground rod under the meter?
Does the central steel beam need to be bonded?
Larry C
#124627 11/12/06 05:07 PM
No bundling derating issue to even consider if there are less than 9 current carrying conductors in either of those bundles if indeed the AHJ feels they are bundles.
(Mine would)
#124628 11/12/06 06:15 PM
I installed a 125 AMP sub panel in the 2nd floor laundry room. It feeds 5 bedrooms, 1 future bedroom, 2 full baths, master bathroom jacuzzi (20 amp), 2 furnaces, and all 2nd floor and attic lighting. It is full at 20 full size breakers but has the capacity for 40 twins.
That's what I did originally. The boss didn't like it that way and had me change it to how it is now.
Fortuneatly, I got to do the service before the gutters were installed.
The 210.63 requirement is within 25' of the equipment but can't be seen in the picture. It's there though.
No ground rod is needed. The Ufer was available and was used. The copper water pipes are bonded by #4 cu and the water heater is jumped out from hot to cold.
The AHJ had no issues with bundling. He asked me a question about article 250.148 during the rough inspection and was impressed that I knew what he was talking about.
Not sure when the final inspection will be though.
#124629 11/13/06 12:13 PM
Shock, and all,
NEC 334.15(C) In Unfinished Basements. Where cable is run at angles with joist in ubfinished basements , ...2 #6 or 3 #8 directly to lower edge....
Smaller cables SHALL be run either through bored holes in joist or on running boards.
Below the joist NM cable is a violation.
It isn't just support but, protection. People used to use the wires as clothes line and hang wet clothes from wire hangers from the conductors. A real treat when they had K&T wiring. [Linked Image]
Alan--
Alan--
#124630 11/13/06 05:38 PM
Alan, I interpret article 334.15(C) the same way you do. In fact, that is how I originally installed the cables, on a running board until I was told by the builder AND my boss to do it the way you see it is now. Most inspectors around here are ok with this install as long as it can be boxed-out later if a sheetrock ceiling is installed instead of a suspended ceiling.