#124606 11/10/06 11:41 PM
Joined: Oct 2000
Posts: 3,672
Likes: 4
Admin Offline OP
Administrator
Member
Quote
These pictures are from a residence in Bucks County, PA. The owners of the property went on vacation for two weeks, while their basement was filling up with water from a broken pipe. The water rose to the top of the basement ceiling joists.

- HCE727
[Linked Image]

[Linked Image]

[Linked Image]

Horizontal Ad
Joined: Mar 2006
Posts: 52
T
Member
Aaa!

A little scraping with a metal wire brush and she'll be fine.

Joined: Mar 2005
Posts: 1,213
S
Member
What I find amazing is that nothing in there tripped. They probably ran the sump pumps off electricity from that panel!

Joined: Dec 2001
Posts: 2,516
Likes: 1
T
Member
What does that tell us?
Tap water is often less conductive than you'd think!

Joined: Apr 2004
Posts: 812
Member
Wow. Good point Ranger. What township/borough was this in?

Ian A.


Is there anyone on board who knows how to fly a plane?
Joined: Jan 2003
Posts: 4,391
I
Moderator
Less conductive than many think but still plenty of conductivity to deliver a fatal shock.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Aug 2005
Posts: 214
E
Member
man, those service conductors are freakin' DUST, that thing looks like it was just pulled up from the Titanic!

Horizontal Ad
Joined: Mar 2004
Posts: 391
B
Member
Electrolysis at work, baby! Look at that neutral.

I'm still amazed that nothing tripped, that water would have needed an impedence of better than sixteen ohms to avoid tripping out a 15A breaker on a leg-to-leg fault. Given all the contaminants that I'm sure were floating around in it, I'm amazed it was that resistive.

Maybe the water itself kept the breakers from operating? The cooling would mess up the thermal characteristics and the water itself would foul the mechanism?

On a side note, can you imagine coming home and opening your basement door to find water lapping at the top step? That must've been horrifying.

-John

Joined: Nov 2005
Posts: 187
Member
'Kid, this is in Bensalem.


Hank
Joined: Dec 2001
Posts: 2,516
Likes: 1
T
Member
Quote
On a side note, can you imagine coming home and opening your basement door to find water lapping at the top step? That must've been horrifying
To some extent I can... About 1 1/2 years ago I came home to a sound of heavily running water. When I went down into the dark basement fumbling for the light switch I thought: "What's that weird feeling around my shoes???" Looked down to realize I was wading in almost 2 inches of water...

Some ingenious kid had turned on the sink at full blast, filling it with more water than the drain could take... go figure. Took three of us more than half an hour with buckets and shovels.

Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
558,663 Are you busy
432,946 Re: Forum
401,943 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5