#123634 - 04/18/06 04:10 PM Receptacle Placement  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,456
NY, USA
Quote
This bedroom has far more than the minimum required number of receptacles, yet, old habits die hard....

The first pic shows a receptacle placed right next to the closet door, in the path of other doors. It appears that the guy measured 12 ft from the previous receptacle... and ran out of space, so next to the door it went! I think we can agree that placing it on that blank wall would have been a better choice.
[Linked Image]
Quote
The second pic shows receptacles - and phone jacks- placed on either side of where the bed is certain to go. I do tire of finding receptacles placed dead center, behind furniture!

- renosteinke
[Linked Image] [


Tools for Electricians:

#123635 - 04/18/06 06:40 PM Re: Receptacle Placement  
Alan Belson  Offline
Member
Joined: Mar 2005
Posts: 1,803
Mayenne N. France
Always a dilemma in deciding where to place receptacles [sockets], especially in bedrooms, given that occupants might decide to move the furniture around someday. To a large extent the position of outlets sets the layout of most room furniture, ie tv aerial, phone socket, pull switches at a bed etc..
What is the significance of '12ft', BTW? Is this a Code requirement?

Alan


Wood work but can't!

#123636 - 04/18/06 07:45 PM Re: Receptacle Placement  
kale  Offline
Member
Joined: Nov 2002
Posts: 174
At least the one near the closet won't be hidden by furniture, so there'll be someplace to plug in the vacuum cleaner.


#123637 - 04/18/06 09:27 PM Re: Receptacle Placement  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
The one near the closet is almost a slam dunk for a night light.
Oooo, I stubbed my toe [Linked Image]


Ron

#123638 - 04/18/06 09:50 PM Re: Receptacle Placement  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Alan, our code has, for a very long time, mandated that residences have the receptacles spaced so that no point along the floor, where the floor meets the wall, is more than six ft. from a receptacle.
Receptacles on the floor, within 18" of the wall, and wall receptacles 5'6" or lower are considered in meeting this requirement.

The effect of this rule all too often is poor receptacle placement. The electrician will enter the room, measure off six ft. from the door, then start placing receptacles on a 12-ft spacing. All too often, (since most rooms are 12x12. or smaller), is that the receptacles wind up in the middle of, and behind, furniture.


#123639 - 04/19/06 11:06 AM Re: Receptacle Placement  
mil28094  Offline
Junior Member
Joined: Aug 2002
Posts: 7
Jacksonville Florida
Alan,

Years ago when I was first starting out in the trade, I asked my journeyman the same question. He told me that the reason for the 12 foot rule was that a table lamp has a cord that is 6' long. With the 12' rule, then a person could always be within the reach of a receptacle behind a large piece of furniture such as a couch/sofa without having to use an extension cord.

I do remember reading this later on in my career, but right now I can't recall exactly where it is located in printed word.


#123640 - 04/19/06 12:09 PM Re: Receptacle Placement  
RSmike  Offline
Member
Joined: Nov 2002
Posts: 134
Holland, MI USA
Kale and Ron,

You guys are so on the money with this. I hate it when I have to search to find receptacles for "temporary installations" like vacuuming. The code should add a note that says to add two more above whatever amount you figured out plus one more for a nightlight. [Linked Image] I have a couple in my house that are only there for vacuuming and nightlighting.....

Has anyone ever been called back because you put in too many receptacles. I know, I know.... they cost money.

RSlater,
RSmike


#123641 - 04/19/06 02:02 PM Re: Receptacle Placement  
ghost307  Offline
Member
Joined: May 2005
Posts: 907
Chicago Illinois USA
RSmike, you have the same idea that I do. Even though the constant crying of "what's the absolute bare minimum that I have to have by the strict letter of the Code" has been getting on my nerves for years, I like to think that I try to consider the people LIVING in the space.

I've been told EXACTLY where the cable TV goes, but get snapped at for adding cost to the job when I try to make sure that there's a receptacle right next to it.

BTW, If the first picture in the post was of MY house, that receptacle would be right where it is...for the vacuum; I'd place another on that blank wall for whatever table or cabinet ends up at that location.


Ghost307

#123642 - 04/19/06 08:25 PM Re: Receptacle Placement  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
It's a poor design IMO. I understand the NEC is the bare minimum requirement, but at least have a clue about the meaning of convience outlet. But in today's world (especially new residential) it's much too cut throat and bare minimum is a must. I work as if the house I'm wiring is mine, always.


#123643 - 04/21/06 11:44 AM Re: Receptacle Placement  
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,400
Vienna, Austria
Regarding the vacuum cleaner issue... one possible remedy would be to invent single gang switch plates that take a toggle switch and single NEMA 5-15 receptacle along with matching devices (either single part or maybe despard style but for upright mounting) and always install one of those at each door. The receptacle is unlikely to be used permanently, being rather high above the floor, so it can be used for temp. stuff.


Page 1 of 3 1 2 3

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 