egc's #12347 08/08/02 01:03 AM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
egc = equipment grounding conductor

residential kitchen, small appliance bc in 2 gang box with switch leg for light..... crimp sleve the egc'c for both, or keep them separate? why?

also is there a code restriction to not cut off one of 2 tails from an egc crimp sleve? or is just one tail ok for the device? thanks

Work Gear for Electricians and the Trades
Re: egc's #12348 08/08/02 07:43 AM
Joined: Jul 2002
Posts: 175
E
electric-ed Offline
Member
bc = ????

Re: egc's #12349 08/08/02 08:15 AM
Joined: Mar 2002
Posts: 95
J
joeh20 Offline
Member
branch circuit=bc???
just joes guess here small appliance branch circuit


Lighting the way
Re: egc's #12350 08/08/02 08:36 AM
Joined: Nov 2000
Posts: 2,236
sparky66wv Offline
Member
Still no decoder ring...

[Linked Image]

All equipment grounds in a box are to be bonded (spliced) togther, even if they are on different circuits. This is NOT to be mixed up with noodles, for they should remain independant from other circuits.

Even though it isn't widely enforced, the 6" free conductor length also applies to EGC's, so the shortest one has to be 6" (with 3" available outside the box).

Sorry, book's in the truck, I'm lazy this morning, so no code refs...

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: egc's #12351 08/08/02 08:38 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
Cindy,
250.148 tells me that all EGCs must be joined together.
With multiple devices in a box, leaving the multiple tails on the EGCs makes it easy to ground the devices.

Re: egc's #12352 08/08/02 08:46 AM
Joined: Oct 2000
Posts: 3,960
Bill Addiss Offline
Member
joeh20,

Good Call!
I was wondering about 'bc' myself.

[Linked Image]
Bill


Bill
Re: egc's #12353 08/08/02 09:42 AM
Joined: Oct 2001
Posts: 597
E
ElectricAL Offline
Member
Cindy,

As to the "why" for tying the egc of one circuit to another (or others). . .this creates multiple parallel return paths for fault current. The egcs form a net or web. The overall resistance of the egc is reduced by the parallel resistances.

Al


Al Hildenbrand
Re: egc's #12354 08/08/02 03:14 PM
Joined: Jun 2002
Posts: 41
W
WNYJim Offline
Member
I use Buchan spice caps for the EG. Slide the cap over long ground leads (after twisting them together). Leave one lead for each device and if it’s a metal box leave one for that also. Then cut off the remainder.
Also on rough in, I like to group the leads for each device and do a “barber pole” wrap with the ground wire.

Re: egc's #12355 08/08/02 09:27 PM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
sorry, i must be the worst at over-using abbreviations here

some tie all egc's together, and some only tie the 12awg's together and put the 14awg's together in separate crimp sleeves, 250.148 seems to say all egc's are to be tied together, but it says "where circuit conductors are spliced" so i guess they could argue that it doesn't say "where DIFFERENT[12awg, 14awg] circuit conductors are spliced" they have to be spliced together. so if all ciruits with egc's in a plastic box are required to be spliced together, why doesn't it get turned down by inspectors? i just saw this today.

Al, thanks, that's a different way of looking at the parallel path idea for me. i always thought of parallel paths as bad things.

about the decoder ring thing.
maybe over in the left margin with the advertisements we could have a quick easy reference decoder ring listing of abbreviations of the top ten or so, think of all the bytes we could save [Linked Image] my votes are for these.
GEC grounding electrode conductor
GC grounded conductor
UGC ungrounded conductor
EGC equipment grounding conductor
BC branch circuit
OCPD overcurrent protection device


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
BigB 3
NORCAL 3
Popular Topics(Views)
270,046 Are you busy
204,436 Re: Forum
192,645 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3