#123290 - 03/14/06 01:00 AM 200A Panel and Sewage Ejector  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,458
NY, USA
Quote
This is a 200A panel and a sewage ejector panel that I did in a new home, someone will find something wrong about them.

- HCE727
[Linked Image]

[Linked Image]

[Linked Image]


Tools for Electricians:

#123291 - 03/14/06 01:45 AM Re: 200A Panel and Sewage Ejector  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
is that first photo related to the tank alarm for sewage pump ?? but one thing it bother me a bit where is the switch to control it or hardwired to breaker box ??


on third photo above the 200 amp box i am not sure if my eyes are teaseing me or not but i did see wrong kind of wire staple on romax look like 3 or 4 is with one staple is too much

the other question i dont know if this is correct answer or not but where is ground wire is is that hidden in pvc or emt ?? hard to see it


Merci , marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#123292 - 03/14/06 06:02 AM Re: 200A Panel and Sewage Ejector  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I think it looks great. [Linked Image]

In some areas that would not pass as some areas prohibit running NM / SE exposed below about 8'.

What you have there is a typical installation (although neater) in this area and I have yet to see the NM damaged when used like this.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#123293 - 03/14/06 09:52 AM Re: 200A Panel and Sewage Ejector  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
I think it looks great too.

The only thing I'd have done differently is use RNC for those 2 circuits going left and right near the bottom of the panel along the concrete wall. To me, that IS subject to physical damage.

I'd also have preferred using RNC/ EMT instead of the running board used at the sewage ejector panel.


#123294 - 03/14/06 10:41 AM Re: 200A Panel and Sewage Ejector  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I agree....only some little quibbles.

Here romex, when run exposed, has to be protected (in pipe) until 7'6" above the floor.

Good eye, Marc....apart from that staple holding way too many cables (look at the way the legs are spread), some of the cables appear to be stapled 'on edge,' a code violation.


#123295 - 03/14/06 12:19 PM Re: 200A Panel and Sewage Ejector  
HCE727  Offline
Member
Joined: Nov 2005
Posts: 186
Delaware County, PA, USA
Sewage pump is hard wired, the grounds are to the left of the se, I was never shot down for cables below 8', circuit on right is emt, circuit in left was done by the well water co., only 2 wires per staple.


Hank

#123296 - 03/14/06 05:44 PM Re: 200A Panel and Sewage Ejector  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
HCE : if you dont mind this again but please look at the 12-2's romex on left side there is 4 of them and one 14-2 romex with ONE staple [ unforetally i cant able to get one photo enlarged and high lighted where to look for it]

so please look at the cable again and tell me how many romex's in one staple

[Linked Image]

[This message has been edited by frenchelectrican (edited 03-14-2006).]


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#123297 - 03/14/06 06:24 PM Re: 200A Panel and Sewage Ejector  
TNTELECTRIC  Offline
Junior Member
Joined: Feb 2006
Posts: 9
CENTRAL CITY, KY, USA
NEAT LOOKING WORK. IS THAT A DOORBELL TRANSFORMER AT THE BOTTOM OF THE PANEL I WOULD GET NAILED IF I DID THAT. BUT OTHER THAN THAT EVERYTING LOOKS FINE TO ME.

TOM


#123298 - 03/14/06 08:11 PM Re: 200A Panel and Sewage Ejector  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
I see alot of panels on this forum mounted to wood thats mounted to the cement wall.

Whats with the wood? How come the panel itself mounted to the wall. Seems like extra work.

I also agree the 12-2 on the left going to the GFCI should be protected.. same with the one below the panel. Other than that looks great.


Shake n Bake

#123299 - 03/14/06 08:58 PM Re: 200A Panel and Sewage Ejector  
HCE727  Offline
Member
Joined: Nov 2005
Posts: 186
Delaware County, PA, USA
Frenchie, on the left side there is a 10/3, 14/3, 2-12/3's with a bigger staple.


Hank

Page 1 of 2 1 2

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803