Besides of wiring completely wrong, It looks like instant fireworks here, if each conduit represents a phase each. Also its undersized for 1600 Amps anyway.
Then it's a fire hazard in on this wooden panel. CT's supposed to be in a sealable metal enclosure.
Very poor protection on these, I think PT fuses wiring.( red orange grey ) A fault on these will evaporate the latter, there the fuses are not mounted nearby the point of supply.
The product of rotation, excitation and flux produces electricty.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
No bonding either
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Am I interpreting this correctly? All the cables in the first conduit are connected to the xfmr A-phase, all in the second to B-phase, and so on? How on earth could he think that's right? [This message has been edited by pauluk (edited 01-30-2006).]
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
This is scary! This is what separates mechanics from electricians.
I don't even see locknuts on the bottom conduits.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Nov 2002
Posts: 794 Likes: 3
Member
|
If he was consistant with the color codes on the wires, it looks like he did not separate each phase in its own conduit. But each current transformer will only see a difference of source and return currents, like a giant GFCI. That would make for very low power bills And this guy does work for the POCO? (I assume that these transformers are for measuring power consumption for billing?). Or is it that that he wired each conduit and current transformer so they see only one phase, ignoring his color codes? Then there are dead shorts between phases at the terminals in the upper parts of the picture, where the red and blue coded wires connect? [This message has been edited by wa2ise (edited 01-30-2006).]
|
|
|
|
Joined: May 2005
Posts: 178
Member
|
Larry, I see no locknuts, either, and no bushing on the 4th conduit. It was just too close to the middle conduit to thread anything onto it. Poor supervision during the initial conduit placement, I suppose.
That's the sort of thing that makes me furious -- it would have been trivial to place the conduits correctly in the first place had someone paid even a little attention. Since they didn't, it becomes impossible to make it right later. Like a bird turd hitting a snowy slope and starting an avalanche.
So, all those cables in the 5th (rightmost) conduit must be connected to the transformer neutral lug, and that's why they don't pass through the CTs on their way to shorting everything the hell together. There's just so much wrong here, it's amazing.
|
|
|
|
Joined: Jan 2006
Posts: 4
Junior Member
|
Well the first thing to say is the CT cabinet is ok it is open right now to take the picture. The ridged conduit coming up in the can is tied to PVC in ground all the way to the xfmr. And the xfmr is bonded correctly, and there is a grounding bar on the right of the CT cabinet that the meter ground #6 solid is going to, you just can't see it becuase of the door being open. this CT cabinet is also located inside the electric room.For those who thought it was outside.
Glad to be here, thank you for for the welcome
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
JAKEE, Which one of the wrong ways were the conductors connectred? Dead Short, or Cheap Metering?
|
|
|
|
Joined: Jan 2006
Posts: 4
Junior Member
|
|
|
|
|
Joined: Dec 2004
Posts: 354
Member
|
How flammable is that wood its all mounted on ?
Thats the worst CT chamber I've ever seen.
Is this work subject to inspection ? How did it pass ?
|
|
|