ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
2017 NEC Changes
by HotLine1. 12/11/17 12:10 PM
Casino Wiring methods
by HotLine1. 12/09/17 10:44 AM
Ground wire Size to water Line.
by HotLine1. 12/05/17 12:11 PM
Flexible conduit to an outside Spa
by gfretwell. 12/05/17 12:28 AM
Dimmable LED 2x4 lay in fixtures
by Vulsion. 11/30/17 06:37 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
243,014 Are you busy
179,414 Re: Forum
170,373 Need opinion
Who's Online Now
0 registered members (), 27 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#121688 - 08/08/05 09:03 PM 300.11, Support From Suspended Ceilings  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,460
NY, USA
Quote
As I read 300.11, we are not allowed to use the ceiling grid to support out pipe and boxes.

As this pic shows, some firm went to great lengths to manufacture assorted connectors for this specific purpose.

I look at B-Line's catalog shows they make a variety of such connectors (such as model BA-14).

So I ask some questions:

---Is it possible that B-Line would manufacture, even list, items that we're not allowed to use?

----Do I mis-understand the NEC? If I'm to apply the NEC, just how do I ascertain the "ceiling system menufacturers' instructions?"

- renosteinke
[Linked Image]

[Linked Image]


Tools for Electricians:

#121689 - 08/08/05 09:56 PM Re: 300.11, Support From Suspended Ceilings  
Tiger  Offline
Member
Joined: May 2005
Posts: 706
Crystal Lake, IL USA
I wouldn't expect the manufacturer of the ceiling system to have any instructions for electrical installations.

IMO the UL listing of materials certifies that it "dies" in a safe manner, not that it is proper material according to the NEC.

I'd like to see the item you mentioned. I don't have their catalog.

Dave


#121690 - 08/09/05 04:32 AM Re: 300.11, Support From Suspended Ceilings  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Not everyone uses the NEC as written, here in MA I can support electrical equipment from the ceiling tie wires. (Non-fire rated ceilings)

MA amended much of 300.11


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#121691 - 08/09/05 06:54 AM Re: 300.11, Support From Suspended Ceilings  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,262
Fullerton, CA USA
Quote
Not everyone uses the NEC as written

Bob's right. Both B-Line and Caddy sell to an international market.

The Caddy catalog has the disclaimer ..."check with local authority for application approval" on most of these items.

Cooper/B-Line has a different catalog for Europe, Asia, and Africa than that for the Americas.


#121692 - 08/09/05 11:16 PM Re: 300.11, Support From Suspended Ceilings  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Just so no one get any ideas....This install is in the exoctic locale of Reno, Nv.
As for catalogs, I got the part number from the on-line catalog for North America.
Another thread (in the general forum, I think) mentions the Caddy part numbers.



Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7709 MB (Peak: 0.9109 MB) Zlib enabled. Server Time: 2017-12-12 17:54:11 UTC