ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Forum Updates Coming Soon.
by Admin - 08/18/19 01:55 PM
Anybody Remember this?
by Bill Addiss - 08/17/19 09:07 PM
Fuse blower plug?
by Bill Addiss - 08/17/19 09:01 PM
100 year old Light Bulb
by Bill Addiss - 08/17/19 11:44 AM
1897 paper on 110-220 incandescent lamps
by ghost307 - 08/15/19 10:31 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 13 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Lost a Phase, Burnt Meter Pan #120446 04/10/05 12:03 AM
Joined: Oct 2000
Posts: 3,575
Admin Offline OP
Administrator
Member
(posted for richard)

the meter with the line side burnt up, probably from water damage

[Linked Image]

[Linked Image]

[Linked Image]

threaded aluminum conduit on roof:

[Linked Image]

[Linked Image]

[Linked Image]

Tools for Electricians:
Re: Lost a Phase, Burnt Meter Pan #120447 04/10/05 12:05 AM
Joined: Oct 2000
Posts: 3,575
Admin Offline OP
Administrator
Member
the line to the building. notice (last pics), the point of attachment is on the sign not the building.

[Linked Image]

[Linked Image]

[Linked Image]

Re: Lost a Phase, Burnt Meter Pan #120448 04/10/05 11:20 PM
Joined: Jun 2003
Posts: 1,143
D
DougW Offline
Member
What comes out of the NEMA box on top of the meter base.... power theft point, perhaps?

Re: Lost a Phase, Burnt Meter Pan #120449 04/10/05 11:30 PM
Joined: Sep 2002
Posts: 883
N
NORCAL Offline
Member
Nasty, hacked up electrical, and that roof pond does not look too healthy either.

Re: Lost a Phase, Burnt Meter Pan #120450 04/11/05 12:54 AM
Joined: Oct 2004
Posts: 803
mxslick Offline
Member
Very fortunate this didn't evolve phase-to-phase and destroy the riser.

Agree with DougW, what's up with the can above the meter base? Hack substitute for a proper hub maybe?

edit: And is that bypass lever engaged and continuing to feed the building?

[This message has been edited by mxslick (edited 04-11-2005).]


Stupid should be painful.
Re: Lost a Phase, Burnt Meter Pan #120451 04/11/05 01:34 AM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
on the second photo i did notice on main lugs above the socket and i did see the diffrent conductor on left hot line lug look like copper wire is there and the rest is alum wire and this socket this is delta service becaue i can tell by hot conductor with red wild leg on right side of it and also the netrual wire it is copper also so this is very instering set up

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Lost a Phase, Burnt Meter Pan #120452 04/11/05 04:36 PM
Joined: Apr 2004
Posts: 156
R
rad74ss Offline
Member
Has anyone checked the gasket on that LB? If that thing starts to crack up due to age/sunlight/heat, the riser turns into a funnel.

I have seen a lot of places with burn outs due to cracked or torn gaskets. Most people don't even think about checking them or changing them out, even though it is relatively cheap versus the cost of replacing whole services.

Robert

Re: Lost a Phase, Burnt Meter Pan #120453 04/11/05 06:47 PM
Joined: Aug 2003
Posts: 99
richard Offline
Member
i might get a chance to check out that gasket. my boss has to give a price for repair of this mess


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
GeneSF 8
Popular Topics(Views)
257,860 Are you busy
193,586 Re: Forum
183,222 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3