Breaker Trips after Half-Hour Delay #119846 02/03/05 09:56 PM
Joined: Oct 2000
Posts: 3,631
Admin Offline OP
Administrator
Member
Quote
I went to troubleshoot a tripped breaker, and after taking all the load off of the circuit and putting on one lite at a time, I still could not narrow it down to any one thing. I did find that someone had used a ground for a neutral for the return of about 4amps for some lites(It was done so the homeowner would have a 3way) After about 3 hrs of tracing each wire, this is what was found in a boxed out a/c return.

- richard
[Linked Image]

[Linked Image]

[Linked Image]

Tools for Electricians:
Re: Breaker Trips after Half-Hour Delay #119847 02/03/05 10:55 PM
Joined: May 2004
Posts: 697
D
Dave55 Offline
Member
From the second picture it looks like a nail pierced the NM. Is this what you think happened?

Dave

Re: Breaker Trips after Half-Hour Delay #119848 02/04/05 06:00 PM
Joined: Aug 2003
Posts: 99
richard Offline
Member
Yes, or a staple. There was a staple next to it. I might have smelled it burning, but the heat was set at about 80, and the return was constantly pulling the air in. They are really lucky.

Re: Breaker Trips after Half-Hour Delay #119849 02/04/05 06:41 PM
Joined: May 2004
Posts: 162
C
cpal Offline
Member
Was that a bed room circuit????

Charlie

Re: Breaker Trips after Half-Hour Delay #119850 02/04/05 07:32 PM
Joined: Aug 2003
Posts: 99
richard Offline
Member
It was in the dining room wall, they had a pipe on the secound floor burst, and the water made its way to the hole in the wire. As the connection between the hot and the ground/neutral was made, the wire heated and the breaker tripped.I think the water could have bubbled, and thats why it took so long to trip.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,631
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,784 Are you busy
204,997 Re: Forum
193,113 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3