This looks like a perfect illustration of the reason that <1000 amp WYE services require GFPE!
In this case, wouldn't the GFPE be located in the building's switchgear? Since these appear to be the service conductors the GFPE wouldn't help.
[Edit: Iwire's post went in as I was typing this
]
Something on the idea of a cable limiter that utilities use would do the trick. It would have been located at or in the padmount.
Originally I was going to remark that better fuse coordination by the utility would have limited the damage, but it's possible that depending on the primary connection the fault current seen by the primary wasn't high enough to open the fuses at the start of this fault. (Thinking delta/Wye).....
We do not know the cause here, once our guys get there the cause is unimportant, they just start ripping the old out and replacing it.
Please do not take this the wrong way, I mean no offence here,
but if something like this happened to any installation or repair I was involved with, I would certainly want to know what caused it!
[This message has been edited by mxslick (edited 12-25-2004).]
[This message has been edited by mxslick (edited 12-25-2004).]