A Little Burnt #118579 10/11/04 08:57 PM
Joined: Oct 2000
Posts: 3,632
Admin Offline OP
Administrator
Member
Quote
Here is one that got just a little hot!

- Jwww
[Linked Image]

[Linked Image]

Tools for Electricians:
Re: A Little Burnt #118580 10/11/04 11:44 PM
Joined: Jul 2003
Posts: 394
B
Big Jim Offline
Member
Did that second double breaker develop a pole to pole short? It looks pretty crispy and not a lot of other damage except smoke

Re: A Little Burnt #118581 10/12/04 12:17 AM
Joined: Sep 2002
Posts: 893
N
NORCAL Offline
Member
What is the story behind it?

Re: A Little Burnt #118582 10/12/04 02:50 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Looks like the lower set of breaker buss-work shorted with no trip of the 2-pole feeding it, and/or the main feeding this panel.

Oh wait, is that the main panel? (Notice the bare AL ground on the neutral bar.)

Took the hit till it blew open!


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: A Little Burnt #118583 10/12/04 02:51 AM
Joined: Jul 2002
Posts: 8,346
Trumpy Offline
Member
I'd hazard a guess and say that this has been a sustained fault (Overloaded Circuit+ Faulty Breaker?), judging by the colour on the inside of the panel.
It's strange how the Neutral/Ground Busbars are still silver?. [Linked Image]

Re: A Little Burnt #118584 10/12/04 07:13 AM
Joined: Mar 2002
Posts: 360
T
Trainwire Offline
Member
hmm looks to me like an old FP with no main.

They used the 6 moves of the hand rule and tied the two pole breakers direct to incoming. with one of the two polebreakers feeding the lighting loads. The breaker labeled "main" just shut off the lighting loads.

I'll bet one fried chicken TV dinner that the lower left DP breaker had the contacts arcing and get hot enough to burn the housing. No overload, no short.

The FP fuse panel in my house did the same thing. Dryer fuse got hot enough in normal use that I had to use gloves to pull it.

These people are fortunate that it didn't take the house with it.
TW

Re: A Little Burnt #118585 10/12/04 07:26 AM
Joined: Jul 2004
Posts: 4
J
Jwww Offline
Junior Member
Yes it was the second breaker that developed a short. the wild thing is that it was a 30 amp breaker on the water heater which was wired with 12/2, and there was nothing else burnt on the wiring.

Re: A Little Burnt #118586 10/12/04 08:34 AM
Joined: Apr 2004
Posts: 156
R
rad74ss Offline
Member
This reminds me of a gas furnace at a place I used to work at. It heated the paint booth. Every day it had to be re-lit by hand. I told my supervisor that it needed to be tagged out because it was electric ignition and it was going to blow up if it didn't get fixed.

It was winter so I was told to go re-light it and they would get somebody to look at it. I walk out there with a little propane hand torch since it was to windy for matches, open up the door (the furnace cover plate had been left off by the previous lighter), and lo and behold the panel is black. There was no insulation on any of the wires and little puddles of yellow and red wire nut plastic on the bottom.

I stepped outside and turned off the main and the gas and told the painters they were going to have to suck up the cold for a long time now!

It amazes me how this kind of problem doesn't burn houses down. How could they de-energize that panel?

Re: A Little Burnt #118587 10/12/04 11:14 AM
Joined: Nov 2001
Posts: 745
M
mamills Offline
Member
This event makes a good case for keeping panel doors closed - this one obviously wasn't, as evidenced by the clean condition of the label. It's a good thing that this fault either burned itself clear, or something opened ahead of it. Does a main disconnect exist ahead of this panel?

Mike (mamills)

Re: A Little Burnt #118588 10/12/04 11:30 AM
Joined: Jul 2002
Posts: 8,346
Trumpy Offline
Member
Mike,
Quote
This event makes a good case for keeping panel doors closed - this one obviously wasn't, as evidenced by the clean condition of the label.
Now there is a thinking man!
Good call mate. [Linked Image]

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,960 Are you busy
205,849 Re: Forum
193,925 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3