ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#118497 09/22/04 08:15 AM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Quote
Thought you might get a kick out of this one. I'm doubtful that the Canadian code allows for wire to be buried in concrete, sans conduit, especially in a very very damp location (Vancouver, Canada).

- Derek L.
[Linked Image]

#118498 09/22/04 09:05 AM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Good Lord!.
It makes you wonder what the rest of the cable looks like, inside the concrete.
The chemicals in concrete aren't usually that kind to PVC. [Linked Image]

#118499 09/22/04 10:49 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Mike,
Quote
The chemicals in concrete aren't usually that kind to PVC.
I've never heard that before. The most common underground installation in my area is concrete encased PVC conduit.
Don


Don(resqcapt19)
#118500 09/22/04 11:41 AM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Don,
The type of PVC that is used for rigid conduit, is an un-plasticised version of Poly-Vinyl-Chloride.
The type used for wires and cables has a plasticiser added to it, to make it more flexible.
It is this plasticiser, that the acidic content of the concrete reacts with.
There are also forms of plasticiser that react with sunlight too and some overhead lines here have been known to lose thier insulation.

#118501 09/22/04 01:27 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Thanks Mike.
Don


Don(resqcapt19)
#118502 09/23/04 06:00 AM
Joined: Jul 2003
Posts: 394
B
Member
Nice custom in-use cover also!

#118503 09/23/04 01:11 PM
Joined: Oct 2003
Posts: 172
G
Member
All the conduit is for in concrete is a raceway,if after the cement sets the conduit rots away or disintegrates no matter you have the channel and you must pull a ground.

#118504 09/23/04 03:50 PM
Joined: Dec 2001
Posts: 2,498
T
Member
A guy from germany once told me the Mexican way of resi wiring. Put a greased garden hose into the concrete walls while pouring them. After it's set pull out hose and reuse. Then pull THHN into the resulting cavity. No ground, just a jumper wire N-G at every receptacle.