#118113 08/11/04 09:52 PM
Joined: Oct 2000
Posts: 3,661
Likes: 1
Admin Offline OP
Administrator
Member
Quote
Got a call to a loss of kitchen counter power & encountered this beautiful early 80's edition of the Crouse Hinds overcurrent protection equiptment.... As typical, the contacts on one of the breakers had, as Electure terms it, "Zinsco-itis... or pitting of the busbar... the really nice part was when I pulled the breaker from the panel, the bus came with it! [Linked Image] But alas, the panel was fully de-energized (Thankfully!) One subpanel change, coming up! [Linked Image]

-Randy
[Linked Image]

[Linked Image]

[Linked Image]

Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Don't know your own strength huh?


Mark Heller
"Well - I oughta....." -Jackie Gleason
Joined: Sep 2002
Posts: 909
N
Member
Zinsco-itis? That is a new one, but that affliction seem to affect any AL bussed panel BTW, I pulled a Zinsco W/ CU buss bars this weekend during "the service change from hell". [Linked Image]

Joined: Feb 2004
Posts: 1,437
Member
LOL Mark... Not on this day, wayyy long day before I even got to this!
Rollie, The bus has oxidation on it, most wisible in the 2nd pic... I've found this specific design of breaker (where the breaker attaches to the busbar with that little tiny loop of a contact) to fail nearly as much as Zinsco & their contacts.... At least they tend to fail-safe when they fail though.... I've replaced many Crouse-Hinds 100A main breakers that tripped & just didnt want to reset!

-Randy


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Top Posters(30 Days)
Admin 10
Popular Topics(Views)
280,481 Are you busy
213,569 Re: Forum
200,439 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5