CATV cable #11806 07/23/02 04:02 PM
Joined: Jan 2002
Posts: 54
M
mountainman Offline OP
Member
This is for all the inspector members and anyone from U.L. I just inspected a satalite installation on a high rise were the cable was dropped down 13 stories in a riser. The cable is marked CL2P and CATV. I cannot find in article 820-53 were CL2P is the same as CATVP. Can anyone help me out with this?

Work Gear for Electricians and the Trades
Re: CATV cable #11807 07/23/02 07:13 PM
Joined: Jul 2002
Posts: 4
D
Dana Offline
Junior Member
Shouldn't the cable be marked as a riser "R" rather than a plenum "P"?
The listings aren't the same unless marked as dual purpose.
N.E.C. also specifically prohibits type CATV as riser or plenum cable [820-51 (c)].

Re: CATV cable #11808 07/23/02 08:53 PM
Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
300.19 is not mentioned in 820.

Should vertical support be considered for 13 floors?

Glenn

Re: CATV cable #11809 07/25/02 02:34 AM
Joined: Oct 2000
Posts: 2,721
Scott35 Offline
Broom Pusher and
Member
Just looking at figure 725-61 [cable substitution hierarchy] from 1996 NEC article 725-61, it says CL2P may be sub'ed for CL2R, and CL2R is listed for use in vertical riser runs penetrating more than one floor.
It also directs from the MPP / CMP box to the CL2P box, which flows out to the CL2R stuff, which is covered in the MPR / CMR section.

Looking at table 820-53 [96 NEC] the permitted sub's for Cable Type CATV include CMP and CMR.

FYI, the "2" in the listing is designating it for use as Class 2 cable

Scott S.E.T.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: CATV cable #11810 07/25/02 05:06 PM
Joined: Jul 2002
Posts: 4
D
Dana Offline
Junior Member
Well, Mountainman, looks like they've put the wrong cable downhole.
Hope they come up with a satifactory resolution for you. (Which in my opinion is "Sorry, but it has to be replaced. And it probably should have support wedges on the top, 5th and 9th floors too. Let's check the data sheet from the mfgr." Thanks gwz).
As an aside, which code was the building constructed to? I presumed the 99 when I posted my first reply.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,918 Are you busy
204,351 Re: Forum
192,571 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3