#116896 05/02/04 05:25 PM
Joined: Oct 2000
Posts: 3,669
Likes: 2
Admin Offline OP
Administrator
Member
Quote
These are pics of a ceiling fan, which the homeowner told me was installed by the previous homeowner... The wire running the fan is none other that "thermostat wire"! [Linked Image] I advised her to keep it unplugged until she could have the installation done properly! Coincidentally, This wire is also running 2 other ceiling fans besides the one pictured...

-Randy (aka Lostazhell)
[Linked Image]

[Linked Image]

[This message has been edited by Webmaster (edited 05-02-2004).]

Joined: Aug 2002
Posts: 1,081
T
Member
No. Can't be. No way. NO way. NO WAY...

Joined: Dec 2000
Posts: 4,289
Member
Randy,
Is this is in a mobile home?

Joined: Aug 2002
Posts: 1,691
S
Member
Just how _thin_ is T-stat wire?

Is it about the same size as bell wire used for telephones? I'm amazed it hasn't overheated and melted. [Linked Image]

Nice heavy-duty plug....too bad they couldn't have at least used heavy-duty cord if they were going to do that sort of stupidity.... [Linked Image]

Joined: Feb 2004
Posts: 1,438
Member
Scott.... Yes it is [Linked Image]

Sven.... Typical T-stat wire is 18-22AWG Solid.. typically 2 pair in a cable like this... I was amazed myself!, considering this stuff is only rated for 24V! & this was running ceiling fans in 2 other rooms! [Linked Image]

-Randy

Joined: Mar 2004
Posts: 391
B
Member
Don't you guys recognize a combination unit when you see one? That is a fan system plus surface mount radiant heating! [Linked Image] [Linked Image]

That really is incredible. I bet those fans turned at about one revolution per year on their highest setting....

-John

Joined: Sep 2003
Posts: 650
W
Member
Guys, have you ever looked up the ampacity of 18ga wire???

20ga wire will _easily_ carry the current needed to run a fan. The voltage drop won't even be too bad if the length is less than a few 10s of feet.

When following the NEC (as well as good engineering practise), circuit conductors need to be sized to carry the load current, to have long useful life without failure, to survive expected faults, to remain safe even in fault conditions, etc. If you give up all of these various safety enhancements, you will still have a system that works.

If running 16A through 14ga wire resulted in instant fire, there would not be all that many hack electricians around, [Linked Image] and we would never be able to have fun discussions about tap conductor rules. [Linked Image] [Linked Image] [Linked Image]

-Jon

Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
If you give up all of these various safety enhancements,

[Linked Image] LOL [Linked Image]

Yeah those darn 'safety enhancements' burn up my time and waste our natural resources. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Feb 2004
Posts: 1,438
Member
Bob,
All those darn safety enhancements put food on my table & pay the bills! [Linked Image] If people started figuring out how to do things the right way on their own, the service industry would'nt be half as lucrative! Not to mention we wouldn't have half as many photos to bicker about here! [Linked Image] I guess the good thing is, that people call us to make things work again, we have a chance to make some difference, maybe talk a little sense into the DIYer, explain "why" things are supposed to be a certain way.... I do it almost daily! Thankfully, I've only been called a couple times for repairs after an actual fire.. & I've seen so many more things that made me wonder why they weren't ablaze already!

-Randy

Joined: Apr 2001
Posts: 518
J
Member
I just installed such a fan yesterday.
The motor was rated at about 1.5 amps, plus a 60 watt bulb. So, we're looking at 2 amps total. Three such fans would be about 6 amps.
From an engineering standpoint ONLY, #18 wire ought to be able to handle about 7 amps. Therefore, I'm not surprised that this unit ran fine, or that there are no signs of overheating.
Of course, there are still the issues of insulation rating, mechanical protection, and short-circuit protection. The breaker is still let 20 amps go through the 7 amp wire- which would allow the wires to imitate toaster filaments.
Need to be fixed? Absolutely. End of the world? I don't think so.

Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,669
Joined: October 2000
Top Posters(30 Days)
Popular Topics(Views)
288,242 Are you busy
220,308 Re: Forum
206,295 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5