Wireway the Rightway #116737 04/20/04 08:24 PM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
Quote
These are intended to complement the "Is there a better way" thread. I did this a few years ago and had the same dilemma. This was GE switchgear with all the branch panels for the space mounted inside the switchboard. The electrical plans called for the gutter and the engineer wanted it. (I found it to be a waste in this case because it isn't legal to use it for what they intended) As you can see I was very careful to keep the conduits over the area they needed to terminate. That doesn't always work out for the best on the other end so I ran everything on a double strut rack to help facilitate turning out to the home run location. Some of the cross sections of the gutter look pretty crowded but they don't exceed 30. It takes allot of planning and it's very tempting to just hit the gutter and go. However, I don't want to do all that work and then get called for it and have to eat the re work!

Nick


[Linked Image]


[Linked Image]


[Linked Image]


[Linked Image]

Tools for Electricians:
Re: Wireway the Rightway #116738 04/20/04 10:50 PM
Joined: Feb 2004
Posts: 1,432
Lostazhell Offline
Member
Nick
You ARE da man! [Linked Image] I rarely see conduit work that takes on a new meaning of "craftsmanship"!
It looks like you evenly spaced all your KO's into the gutter! [Linked Image] How long did that take?
Things like this kinda make me feel "green" again! [Linked Image]

-Randy

(Edited cause I can't read this late LOL)

[This message has been edited by Lostazhell (edited 04-21-2004).]

Re: Wireway the Rightway #116739 04/20/04 11:04 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
Nick, that is a very clean installation.

Do you buy gutter without knockouts and cut them in the field?

Re: Wireway the Rightway #116740 04/20/04 11:44 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline
Member
Bjarney,
Absolutely. I cant figure out why they still sell gutters and pull boxes with concentric KO's any more. They are just in the way 95% of the time.

Re: Wireway the Rightway #116741 04/21/04 06:33 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Great looking work Nick. [Linked Image]

Quote
I can't figure out why they still sell gutters and pull boxes with concentric KO's any more. They are just in the way 95% of the time.

I could not agree more, [Linked Image] any commercial / industrial equipment should come without KOs.

We try to get all we can without KOs but many times it is not a stock item. [Linked Image]

Sometimes it is almost imposable to do a professional looking job because of the factory KOs.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Wireway the Rightway #116742 04/21/04 07:52 AM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
Great stuff, Nick!
It's sure nice to see something like this after the poorly-planned installations I've run across.
The key is in the planning...The old "Measure twice, cut once".

Blank endwall panels and "-NK(no knockout)" wireways and boxes are worth any extra time and effort it takes to get them. There's not much use for those concentric KO's.

Re: Wireway the Rightway #116743 04/21/04 09:42 PM
Joined: Jan 2002
Posts: 5
J
jetlei98 Offline
Junior Member
Could you tell us how long it took and how many guys it took too.

Re: Wireway the Rightway #116744 04/21/04 09:55 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
electure—I agree with you on the plague of concentric (and eccentric) KOs. Talking to switchgear-manufacturing engineers—they dislike them too, for ‘one-pass’ punches and dies are a constant headache to keep sharp on the production line.

Re: Wireway the Rightway #116745 04/21/04 10:59 PM
Joined: Apr 2003
Posts: 48
M
mlk682 Offline
Member
Sweet Work!, Thats the type of installation I walk by and stare at for a few ! Just had to add my two cents!

Re: Wireway the Rightway #116746 04/23/04 07:26 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline
Member
This was done a few years ago so I don't remember exactly how long it took. It was done by myself and a JW. He did all the pipe you see in the photos. There is something in the pics I thought someone might pick up on and bust my chops for but it's probably not obvious because of the resolution of the pics. I have the answer but lets keep it interesting and see if someone can pick it out!
(Hint: The wall you see is 18 Gage steel studs and 5/8 drywall)

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,961
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,031 Are you busy
205,036 Re: Forum
193,149 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3