Sizing an Underground Box #116567 04/11/04 08:31 PM
Joined: Dec 2000
Posts: 4,286
electure Offline OP
Member
Quote
Could someone please help me with the box fill calculation for this splice kit! I unearthed this "splice kit" on a service trouble call. The home was built by a plumber in the 60's.

Jeff N.


[Linked Image]

Tools for Electricians:
Re: Sizing an Underground Box #116568 04/11/04 09:19 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
What's the problem with that?

12 fluid ounces = 21.65 cubic inches.

[Linked Image]

Re: Sizing an Underground Box #116569 04/11/04 09:44 PM
Joined: Aug 2002
Posts: 1,691
S
SvenNYC Offline
Member
That looks like a steel beer can. You probably won't have that problem of aluminium and copper reacting and corroding. [Linked Image]

Last time I saw one of those (it was a Pepsi Can) I found as a kid digging through a pile of garbage for recyclable aluminium soda cans to sell at the supermarket for the nickel deposit back in 1989 or something like that. My mom threw it out a few weeks after I brought it home. [Linked Image]

Take the can, wash it and see if you can sell it on Ebay for a couple of bucks. No joke.

I wonder how many cans of beer said "plumber" had drank before he thought up this little gem...

[This message has been edited by SvenNYC (edited 04-11-2004).]

Re: Sizing an Underground Box #116570 04/11/04 11:37 PM
Joined: Jun 2003
Posts: 1,143
D
DougW Offline
Member
It's in better shape than some "listed" boxes I've discovered!

Re: Sizing an Underground Box #116571 04/12/04 12:45 AM
Joined: Feb 2004
Posts: 1,436
Lostazhell Offline
Member
ROFL.... Thats cool! [Linked Image] I found a ton of those beercans under a house about a year ago while running a bond for the water system... I've never actually seen one being "used" in such a manner though!
If he'd used a "tall boy" he would've had room to cap off the white conductor to the left also! [Linked Image]

-Randy

Re: Sizing an Underground Box #116572 04/12/04 06:56 AM
Joined: Oct 2003
Posts: 289
:
:andy: Offline
Member
On vacation in Italy last year, one evening a part of the ~5 y.o. streetlamps along a sidewalk on the beach went dark. The next day, two italian sparkies started digging sand away just at our beach place, where one light's pole was placed. I was really amused by what came up. about 1,5 feet deep there was a concrete plate, they removed it, and under there was a small "box" about 1x1x1 ft. looked like made of concrete too, at the bottom was wet sand.

Their splice was 3-phase+n+GND AWG10 or 12 coming and going, and one 1phase+N+GND off to the lamp.
It was just taped!! A specific water-tight box would be prescribed here, at least in GErmany.

so guess how thes fixed it (two wires had shorted in the taped splice).
just opened up everything, and crimped it into ferrules (never seen that type of connection).
tjey just crimped the supply line and the lamp's wires into one side of the ferrule, and the line to the other lamps into the ferrule's other side. Tape-n-done. no more u-boats or anything.
and i was like [Linked Image] , see you again next year.......


I tried to ask them how they located the fault just under this lamp, as they hadn't digged up anywhere else, but neither the ~40y.o. nor the ~20y.o. spook one word of english...


i wouldn't want to live there, unless i'd have my house installed by myself.
i once saw an outdoor splice box, where they did the only-pretwist job... just twisted stranded wires, but no wirenut had ever been there, tape again. hell.




[This message has been edited by :andy: (edited 04-12-2004).]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,256 Are you busy
206,143 Re: Forum
194,135 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3