ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
How's Florida doing with Hurricane Ian?
by Bill Addiss - 09/28/22 12:41 PM
Tough being a lineman's kid
by Bill Addiss - 09/28/22 12:39 PM
GFCI's pops in large numbers
by dsk - 09/26/22 04:35 AM
AFCI’s Revisited
by sparky - 09/24/22 09:58 AM
NFPA Price Increase Coming
by Bill Addiss - 09/23/22 02:22 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 36 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#116547 04/08/04 01:50 PM
Joined: Oct 2000
Posts: 3,671
Likes: 2
Admin Offline OP
Administrator
Member
Quote
Hello All,

Called today to a home which had a close call due to a fire in the PoCo Meter Base.. It appears that the conductors entering the line side were tweaked a little too hard against the entrance hub of the base shorting them out... Better pics to come

-Randy (aka lostazhell)
[Linked Image]

[Linked Image]

[Linked Image]

[This message has been edited by Webmaster (edited 04-08-2004).]

#116548 04/08/04 05:46 PM
Joined: Apr 2004
Posts: 36
S
Member
Ya know this is the prime reason why i look at the condition of the wires entering the weatherhead before touching it. One slight movement and WALLA crispy conductors. [Linked Image]

#116549 04/10/04 06:00 PM
Joined: Feb 2004
Posts: 1,438
Member
Tim, I do the same thing... Especially after doing a looooong 566' pull of 500MCM for a car dealership rebuild I did with a "past" company I worked for... about ¾ of the way, we found something had penetrated one of the wires straight through! [Linked Image] [Linked Image]
On this thing, the black above the meter socket is where the wire burned through the conduit... The Edison triplex also melted in places (wierdly, only where someone had put black tape on it)... Even stranger, My hotstick lit up on the grounded phase of the triplex, I've never had this happen before & makes me wonder how well the PoCo Xfmr is grounded... (The Xfmr is pretty close to original for the neighborhood) ...

Job Security

-Randy

#116550 04/10/04 09:05 PM
Joined: Jun 2003
Posts: 1,143
D
Member
Lostazhell...

be something if the POCOC was inadvertantly using your homeowner's grounding electode as their xformer's (and the neighborhood services w/o proper grounding), now wouldn't it!?

#116551 04/11/04 12:17 AM
Joined: Feb 2004
Posts: 1,438
Member
LoL Doug... In this case it wouldn't have been great in the first place.. Black RMC running from the panel to a galv. water pipe under the bathroom, with some sort of wierd clamp... didn't look very good, lots of rust!.. Wish I'd taken a pic of it, but it was in a really awkward place... Another oddity while I'm thinking about it, We ran an extension cord to a neighbor's garage for power (12awgX50') & I noticed my sawzall sounded like it was really laboring, & my cordless charger kept showing "Line Problems" I was only getting 109V! I already advised SoCalEdison of these things, but as far as I've seen, nothings changed on their end.

-Randy


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
Popular Topics(Views)
297,794 Are you busy
228,531 Re: Forum
213,358 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5