This box is a (Hubbell) Raco 3.5" "Ceiling Box". They've been around since the days of knob & tube wiring. Where would you use this particular box??...S [This message has been edited by electure (edited 11-20-2003).]
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
|
|
|
|
Joined: Dec 2002
Posts: 24
Member
|
Only on a ceiling fixture or wall sconce with a canopy that meets the wire fill requirements.
[This message has been edited by Gus1999 (edited 11-20-2003).]
|
|
|
|
Joined: Sep 2003
Posts: 114
Member
|
Well, it's 4.0 cu in-so it's perfect for old fashioned 14-2 Romex with no ground.
|
|
|
|
Joined: Dec 2000
Posts: 4,294
OP
Member
|
I've seen lots of these above sinks in bathrooms on residential work. Seems that darn plumber always vents straight up, and there's almost always a stud right there...S TG, yes when they enter from a domed fixture. Now, what about the ground wire in the 14-2 romex?? It doesn't count?
[This message has been edited by electure (edited 11-20-2003).]
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
Now, what about the ground wire in the 14-2 romex?? It doesn't count? Not if you cut it off before it enters the box...who needs a ground for a light fixture anyway? (NOTE: That was supposed to be sarcasam...)
|
|
|
|
Joined: Sep 2003
Posts: 114
Member
|
These things always seem to get added onto over time
"You know, I always wanted an outlet there...."
|
|
|
|
Joined: Dec 2000
Posts: 4,294
OP
Member
|
Now, let's deduct 1 conductor for the clamps ...S
|
|
|
|
Joined: Aug 2003
Posts: 173
Member
|
I never use the 3.5" ones and never with clamps.
Ceiling fixture that lands on a joist and sconces that land on a stud. They are some of the best support for heavier fixtures since the mounting point is centered on the box.
Speedy Petey
"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
|
|
|
|
Joined: Oct 2000
Posts: 4,141 Likes: 4
Member
|
I've used these before, and reasoned that the Fixture Dome effectively adds volume to the box that can be divided up for conductor fill. It has been a solution for some tough situations.
But ... strictly speaking, 370-16(B)(1)Exception seems to say that the 'domed luminaire' or canopy space can only be used to avoid counting the fixture wires.