#114961 07/23/03 12:25 PM
Submitted by Joe Tedesco:
Why is the cable taped? This is in a kitchen in a hotel
Joe Tedesco www.JoeTedesco.com
[This message has been edited by Webmaster (edited 07-23-2003).]
#114962 07/23/03 01:49 PM
Looks to me as though the correct connector was not used--it's meant for NM cable, not type AC or type MC. (Although, there are dual-purpose connectors, correct?)
Also, it's possible they didn't use a bushing ("redhead") which should be visible.
How is the box containing the GFCI receptacle supported, by the way?
Also, is the MC cable properly supported?
#114963 07/23/03 05:18 PM
This is something I get after coworkers about, although usually in larger sizes because the connector is not gripping the armor. [Linked Image]
I agree with Think Good here.
Either they had no antishort bushing and used tape in place of it or they had an antishort bushing and needed tape to hold it in place due to the use of a NM connector.
When I tell coworkers not to do this they always will tell me that MC armor is not a grounding conductor and that the box is grounded by the insulated grounding conductor in the MC.
What they seem to overlook is that the armor is a metal raceway that needs to be bonded/grounded.
#114964 07/23/03 05:51 PM
Couldn't find a IG GFCI?
#114965 07/23/03 06:19 PM
Must be one of those cutting-edge hepcat IG-Ultra systems there's been so much buzz about. ;-)
[Oops. That takes orange tape.]
[This message has been edited by Bjarney (edited 07-23-2003).]
#114966 07/24/03 09:16 AM
Hey! That tape for an IG is a great idea, wish I had thought of that. LOL!
Pierre
Pierre Belarge
#114967 07/24/03 01:29 PM
The screws don't appear to be nylon, though... [Linked Image]
#114968 07/27/03 02:26 PM
Yeah, that certainly doesn't seem to be a BX-type cable clamp. The ones I've seen in a certain DIY warehouse are roundish barrels with a set-screw to clamp on the metal jacket and a lock nut for the box.
The opening at the end where the wires exit is designed to hold the red bushing in place.
And yes. They're packed in clearly marked bags that have BX Connector or some such thing printed on them. [Linked Image]
#114969 07/27/03 08:43 PM
i belive there still exists two-screw amored cable connectors on the market, although they have fallen out of vouge.
a redhead is debatable here, i believe it would depend on the conn. listing, but i'm unsure
the cable sheath here is not a grounding conductor, i would however prefer it grounded.
#114970 07/27/03 09:48 PM
There's a kind of "BX" cable that has an aluminium sheath. Instructions and notes that come with it insist that you not use the "setscrew" clamps. But a style clamp that squeezes the sheath, similar to the clamp in the picture.
Anyone ever have the aluminium sheath to clamp connection fail when a serious fault current happened? I'd think you could get a bad connection due to corrosion of the aluminium.