This is often seen where a cable has been cut and must be joined back together or someones' idea of Tapping into a line.
Why is this Bad?

[Linked Image]

Horizontal Ad
Joined: Aug 2002
Posts: 25
J
Member
Back wrapped ECG's and short conductors, exposed hots behind wire nuts. Could have been done with 2 junction boxes spread apart with 2 new pieces of NM to give adequate wire for the 3-6 rule.

[This message has been edited by Joule-E (edited 09-22-2002).]

Joined: Nov 2001
Posts: 745
M
Member
Violations not withstanding, which Joule-e has already mentioned, this thing must have been VERY difficult to put together! [Linked Image]

Mike (mamills)

[This message has been edited by mamills (edited 09-22-2002).]

Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
assuming 1.5"x4" Octagon box and 14 AWG.
15.5 cubic inches / 2 Cu.In. = 7 14 AWG.

314.16.

4 - 2/C NM = 4x2 = 8 x 2Cu.In. = 16 Cu.In.

4 EGC's = 1 EGC = 2 Cu In.

4 Connectors = 1 connector = 2 Cu.In.

Total Cu.In. = 20 Cu. In..

Box is 4.5 C.In too small.

Plus 250.148(A).

Also looks as though some bare Ungrounded conductor exposed at the wirenut, possible 110.7.

Question 334.24.

Appears box was secured to the wood or maybe just a shadow over the bottom hole of the back of box.

[This message has been edited by Gwz (edited 09-23-2002).]


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,400
Joined: April 2002
Top Posters(30 Days)
BigB 6
Jam85 2
Popular Topics(Views)
329,415 Are you busy
254,315 Re: Forum
236,778 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5