Exposed Live Parts #113054
02/19/02 01:20 AM
02/19/02 01:20 AM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,516
NY, USA
[Linked Image]

[Linked Image]

[Linked Image]
Quote
This was found at the rear of some public address equipment that was located in an industrial setting in the Los Angeles area. The line cord runs from the plugmold to the fuse mounted on the rack panel. This is completely in the open, not even so much as a closed rack cabinet! It's also mixed in
with low voltage, and speaker/mic audio lines. It was reported to the technical experts at the site -- now we'll see if they fix it before there is an accident!!

Anomyous

Tools for Electricians:
Re: Exposed Live Parts #113055
02/19/02 01:15 PM
02/19/02 01:15 PM
M
mamills  Offline
Member
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
Even assuming that this rack is located in an area accessible only to qualified personnel, this equipment should be enclosed for a couple of reasons. The first issue is, of course, the presence of dangerous voltage at the fuse protecting the primary of the transformer. In commercial sound systems, it is not unusual to find exposed voltage-carrying components (fuses, 70 and 140 volt speaker output terminal points, filter capacitor cans where the outside of the can itself is intentionally isolated from ground, plate caps on some types of output tubes in older systems which conduct as much as 1000 volts or more). All the more reason why this should be housed in a completely enclosed rack. Simply brushing against some of this stuff can really ruin a person's day... [Linked Image]
The second issue concerns protection from fire. Some components, such as the SS rectifier to the left of the transformer (in the second picture)and some larger resistors in power supplies, can spark upon failure, hence the need for some type of containment. In some sound systems I have installed, I have recommended having a smoke detector attached to the inside of the equipment rack.

It is quite common to find microphone and line-level input cables in the same rack with heavy speaker output and power supply cables. Installers will normally go to great effort to route input cables well away from output and power cables by "dressing" them on opposite sides of the rack as much as possible.

Mike (mamills)


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,416 Are you busy
187,340 Re: Forum
176,680 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9441 MB (Peak: 1.0616 MB) Zlib enabled. Server Time: 2018-09-24 03:44:04 UTC