Name the Violations #112896
10/23/01 09:42 AM
10/23/01 09:42 AM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,524
NY, USA
[Linked Image]
Quote
This was taken at a local home center that is less than two years old. Name the NEC violations!

- Nick

Tools for Electricians:
Re: Name the Violations #112897
10/25/01 09:47 PM
10/25/01 09:47 PM
J
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
Are those xfmrs with the disconnect between them?

Maybe this was wired by the industry 'professionals' that work there?

Re: Name the Violations #112898
10/26/01 07:04 AM
10/26/01 07:04 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,275
Fullerton, CA USA
Although it's kind of hard to tell, it appears that there's no seismic bracing to keep these xfrmrs from rockin' & rollin' in an earthquake. I'd sure hate to be under these when those rods start bending! (Are they hard piped?)

Re: Name the Violations #112899
10/26/01 11:19 PM
10/26/01 11:19 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Sorry about the poor picture quality. Yes they are transformers, and no they are not braced. They are also about 18ft in the air. The secondary over current protection, enclosed circuit breakers are also mounted about 18ft in the air. Not very “readily acceptable. (240-24). I think this also violates 380-8. Some of the disconnects in the store are directly behind the transformers. While it appears from the ground some might meet the clearance requirements in 110-26(a)(1) they have the secondary feeding them from underneath with seal tight 90’s. You couldn’t stand in front of them if there was a platform. Most of them don’t have a chance of meeting 110-26(a)(2). What I really find odd is they went out of their way to provide secondary over current protection for these transformers and just made a mess of it. All the while the panels are directly below them and if equipped with a main could have eliminated the enclosed breakers all together. It looks like they could have meet the 25ft maximum length allowed for transformer taps. I realize that that rule was left out of the ’99 code. But it’s back in for “02! Any inspector that was sharp enough to catch that rule surly would have caught the rest of this stuff.
Who knows what lurks inside! [Linked Image]
Nick


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 98
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,429 Are you busy
188,645 Re: Forum
178,344 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 14 (0.008s) Memory: 0.9606 MB (Peak: 1.0952 MB) Zlib enabled. Server Time: 2018-11-14 09:29:26 UTC