#112896 10/23/01 10:42 AM
Joined: Oct 2000
Posts: 3,671
Likes: 2
Admin Offline OP
Administrator
Member
[Linked Image]
Quote
This was taken at a local home center that is less than two years old. Name the NEC violations!

- Nick

#112897 10/25/01 10:47 PM
Joined: Aug 2001
Posts: 464
Likes: 1
J
Member
Are those xfmrs with the disconnect between them?

Maybe this was wired by the industry 'professionals' that work there?

#112898 10/26/01 08:04 AM
Joined: Dec 2000
Posts: 4,289
Member
Although it's kind of hard to tell, it appears that there's no seismic bracing to keep these xfrmrs from rockin' & rollin' in an earthquake. I'd sure hate to be under these when those rods start bending! (Are they hard piped?)

#112899 10/27/01 12:19 AM
Joined: Aug 2001
Posts: 599
N
Member
Sorry about the poor picture quality. Yes they are transformers, and no they are not braced. They are also about 18ft in the air. The secondary over current protection, enclosed circuit breakers are also mounted about 18ft in the air. Not very “readily acceptable. (240-24). I think this also violates 380-8. Some of the disconnects in the store are directly behind the transformers. While it appears from the ground some might meet the clearance requirements in 110-26(a)(1) they have the secondary feeding them from underneath with seal tight 90’s. You couldn’t stand in front of them if there was a platform. Most of them don’t have a chance of meeting 110-26(a)(2). What I really find odd is they went out of their way to provide secondary over current protection for these transformers and just made a mess of it. All the while the panels are directly below them and if equipped with a main could have eliminated the enclosed breakers all together. It looks like they could have meet the 25ft maximum length allowed for transformer taps. I realize that that rule was left out of the ’99 code. But it’s back in for “02! Any inspector that was sharp enough to catch that rule surly would have caught the rest of this stuff.
Who knows what lurks inside! [Linked Image]
Nick


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,157
Joined: May 2003
Top Posters(30 Days)
dsk 3
Popular Topics(Views)
297,687 Are you busy
228,470 Re: Forum
213,324 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5