#112688 08/18/01 12:53 PM
Joined: Oct 2000
Posts: 2,749
Member
www.joetedesco.com

[This message has been edited by Joe Tedesco (edited 04-15-2003).]


Joe Tedesco, NEC Consultant
#112689 08/22/01 09:39 AM
Joined: Oct 2000
Posts: 2,749
Member
www.joetedesco.com

[This message has been edited by Joe Tedesco (edited 04-15-2003).]


Joe Tedesco, NEC Consultant
#112690 08/22/01 05:28 PM
Joined: Oct 2000
Posts: 5,392
S
Member
George;
I agree, sharp is bad for any raceway, but
I'm not sure of what i'm looking at here, can U explain a bit?

#112691 08/22/01 07:32 PM
Joined: May 2001
Posts: 717
G
Member
Sorry, the pic can use a bit of explanation. I borrowed the contractors sawzall and cut one of the offending bends about 2" on each side of the coupling,you are looking in the center of the assembly, one side Type EB, one side Sched 40.

We got a letter from NEMA, answered through Carlon. They state that the assembly is designed to fit, but the sched 40 should be reamed to eliminate the sharp edge. Field modifications ???? I thought they were not allowed, but apparently I was wrong about that one. It was not an option here, because it was all together already, so the contractor simply replaced them.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Jim M 5
Trumpy 4
Popular Topics(Views)
297,358 Are you busy
228,239 Re: Forum
213,144 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5