#112647 08/19/01 11:43 AM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
[Linked Image]

[Linked Image]

[Linked Image]

3 Guesses who wired this Furnace?
(hint, not an Electrician)

Bill

#112648 08/19/01 04:30 PM
Joined: Oct 2000
Posts: 2,749
Member
1. The mailman?

2. The garbage man?

3. The carpenter?



[This message has been edited by Joe Tedesco (edited 08-19-2001).]


Joe Tedesco, NEC Consultant
#112649 08/19/01 07:03 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Excellent Grounding Continuity though!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#112650 08/19/01 07:36 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Joe,

It was the Plumber!
I thought you were a better guesser than that! [Linked Image]

Bill


Bill
#112651 08/19/01 08:04 PM
Joined: May 2001
Posts: 717
G
Member
And you DIDN'T get a picture of the bend ??????

#112652 08/19/01 08:27 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
The handy box has four empty KO's, so there's room for four more cables, right?

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#112653 08/19/01 09:05 PM
Joined: Oct 2000
Posts: 2,749
Member
Would you reconsider the use of the copper pipe, since it maybe of the type that will comply with rules in Article 680 where "brass or other approved corrosion-resistant metal" is allowed to be used for the wiring methods for some systems.

Search for the term "conduit" and look at the many entries in that Article


Joe Tedesco, NEC Consultant
#112654 08/21/01 07:54 AM
Joined: Dec 2000
Posts: 4,294
Member
Even plumbers are required to strap their pipe!
There's only one strap visible in this whole mess!

#112655 08/21/01 08:41 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
George,

I think the bend was OK,
What I would've liked to check was if the cuts were made with a pipe-cutter and if there was a sharp edge inside.

Joe,

You mean this might be OK?
what about the size itself? This conduit is a bit smaller than our Electrical conduit and doesn't fit in the connectors quite right.

Bill


Bill
#112656 08/21/01 11:53 AM
Joined: Oct 2000
Posts: 2,749
Member
Bill:

Naturally, I would not permit the material you show, but would permit the same material if it was equal in the ID and had threads as any of the Table 4, Chapter 9 wiring methods.


Joe Tedesco, NEC Consultant