ordering wire #11254 07/06/02 05:01 PM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
How much do you add onto your true tape footages for wire orders.

Lets say your pull'n 600's and you got 7 90's (with box in between of course). Do you add 5feet for each nintey and then 10' onto the total footage. whats your method?

One time on the job we were pull'n 600's from basement to roof and the guy on the roof feeding the wire said is it there yet? and the guy at the switchgear said on the radio, no, is it supposed to be???? ( which is was of course) The guy on roof looked like he sh*t his pants.

[This message has been edited by Webmaster (edited 07-06-2002).]

Work Gear for Electricians and the Trades
Re: ordering wire #11255 07/06/02 05:17 PM
Joined: Dec 2001
Posts: 437
The Watt Doctor Offline
Member
E,
On "big" wire pulls, I always pull in a "measuring" tape (I think Greenlee makes them). I add some for "make up", I also add some for making a "pulling head". Every pull is different. If you have a large switchgear that you are pulling into, the "make up" (or termination, whatever you want to call it) will be more. To me the most important thing is pulling a string or measuring tape into the run of conduit. That way mistakes are less likely to happen.

Wired,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
Re: ordering wire #11256 07/06/02 05:43 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
I do the same thing Doc does. (Yes Doc the norm is greenlee)

When your talking this size wire 6'too moch is better than 6" too short.

But, remember 6'* 4= 24' at somewhere in the nieghborhood of $2.50 - $3.00 a foot, is some noticeable wasted money. Imagine this if you were on a job with 20 - 40 of these runs.

Of course you have to build some waste into your bid.

But once again, 24' of waste on a one time pull is probably more cost effective than what you described. [Linked Image]

Roger

Re: ordering wire #11257 07/06/02 08:41 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
I believe Greenlee 435 tape used to have a fairly good "fudge factors" printed on one of the reel faces. They might still be there.

A phone call may pay off… http://www.greenlee.textron.com/support/index.html

Short pulls can surely spoil a Monday.

Re: ordering wire #11258 07/07/02 10:44 AM
Joined: Apr 2001
Posts: 507
G
golf junkie Offline
Member
I measure off the length of the pull as acurately as possible. I don't add for sweeps. I add the actual length for rise and drops.

Then add for your desired tails or waste needed at each end, ( usually 5-10 ft.).

If I am unable to get an exact measurement I will add a little more to be safe.....just depends on how I feel about it.

I usually don't take the time to push in a fishtape and measure it.....allthough I agree this is the most acurate way.

I haven't been short on a big pull.....yet. I have, however, had times where I expected 10' of drop-off and ended up with less than 1'. [Linked Image]

GJ

Re: ordering wire #11259 07/08/02 06:52 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
The Greenlee measuring tape is invaluable for minimizing waste.
The instructions are:
1. Measure the distance from terminal to terminal.
2. Add 12" for each 90 deg. worth of bend.
3. For each pull box, j-box, or cabinet, add an additional (2 x box depth).

(If you are as wacky as I am, add a little more for peace of mind.)

Re: ordering wire #11260 07/08/02 06:26 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
Redsy—I couldn't find that online at their site...would be a handy addition if it's not already there. Only once {fortunately not on my job} have I seen "a sleeve job" on a 1200-foot 4x750-kcmil run. I imagine the compression/heatshrink splices shoehorned a few feet into the duct are fine to his day.

Re: ordering wire #11261 07/09/02 06:39 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
Bjarney,

Go to the Greenlee site (Product info, then Pulling & Fishing)
It's on page 12.

[This message has been edited by Redsy (edited 07-09-2002).]

Re: ordering wire #11262 07/09/02 08:59 AM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
10-4 Redsy...thanks.

Re: ordering wire #11263 07/09/02 10:25 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
The formula is also written on the endcap of the reel.
Rojosy's right, add some for "insurance"

[This message has been edited by electure (edited 07-09-2002).]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,034 Are you busy
205,039 Re: Forum
193,154 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3