200 - 225 #112492
06/29/01 11:02 PM
06/29/01 11:02 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,524
NY, USA
[Linked Image]
Quote
While getting some info for a single-line diagram I found this. Service is 277/480V, 1600A, with a number of 200A &1-400A Fusible Switches. The 400A was fused at 225A. OK. The first 200A Switch was fused at 225A . Huh? I really did a double take on this. The remaining 5- 200A were the same way.
Can you see how they managed this? What would/could happen if these units were called upon to "do their duty?"

Electure

Tools for Electricians:
Re: 200 - 225 #112493
06/30/01 05:35 AM
06/30/01 05:35 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
So U have 225A fuses in many 200A disco's. The result of a 'dead short' and subseqent AIC may see the disco, not the fuses, as the weak link.

Re: 200 - 225 #112494
06/30/01 07:16 AM
06/30/01 07:16 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
But the 225A 600V fuses in the 400A disco are way too large to fit in the 200A switch. [Linked Image]

Re: 200 - 225 #112495
06/30/01 10:00 AM
06/30/01 10:00 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
yes they are, do you suppose there would also be more of a 'flashover' possibility???

Re: 200 - 225 #112496
06/30/01 10:56 AM
06/30/01 10:56 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
I SURE DO see flashover as a problem. There was a hint in my last post, here's another, a little more obvious 110-4. [Linked Image]

Re: 200 - 225 #112497
06/30/01 01:55 PM
06/30/01 01:55 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
no aurgement from me, we could list a few more codes on top of this. my post was stictly speculation, supposing a 'short', not G-fault across two phases fused side by side. they look close!
as a contractor, i find exercising that 'liability node' part of my grey matter to the worst case scenario essential to my survival it's a jungle out there!

[Linked Image]

Re: 200 - 225 #112498
06/30/01 03:43 PM
06/30/01 03:43 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
FRS>FRN, 480>250,(OK, I'll stop this secretive business). These are 250V rated fuses used on a 480V system. They actually fit sickeningly well into the fuse clips. We've included replacing these fuses with 200A, 600V fuses in our bid for the owners' work. If they don't want the work performed, they can't care much about their beautiful 4 story office building.

Re: 200 - 225 #112499
06/30/01 04:41 PM
06/30/01 04:41 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
pardon my ingnorance, now that U mention the obvious, they do look a tad short....

[Linked Image]

Re: 200 - 225 #112500
07/01/01 09:32 AM
07/01/01 09:32 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
I sure hope you're not ignorant, Sparky, because I stood gawking, scratching my head, gawking some more for an awfully long time before I realized what was going on...and I could read the writing on the fuses!! We get so used to seeing things in a certain way that when something looks almost right, it almost passes us by. If you're ignorant, then I'm an absolute moron!

Re: 200 - 225 #112501
07/01/01 10:02 AM
07/01/01 10:02 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
Ok, now that we have established the obvious, as applied to the original Q, what would happen if these fuses were called to duty?
In a worst case scenario ( all i can think of is a dead short), would we have the equivalent of 3 grenades?
[Linked Image]

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,524
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,615 Are you busy
188,750 Re: Forum
178,460 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.033s Queries: 15 (0.006s) Memory: 1.0244 MB (Peak: 1.2003 MB) Zlib enabled. Server Time: 2018-11-19 21:57:16 UTC