Give the rules in the NEC that can be used to cite the violation here.


Joe Tedesco, NEC Consultant
Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

Joined: Jan 2001
Posts: 75
G
Member
300-11(b). It appears smurf tubing is secured to the EMT.

Glenn

Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Octagonal box is crowded?

I'll assume at least 8 conductors...

[This message has been edited by sparky66wv (edited 05-28-2001).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Oct 2000
Posts: 2,749
Member
I would also call attention to the cord connected fixtures where the receptacle is not located properly according to Section 410-30(c) Electric-Discharge Fixtures.
1. A listed fixture or a listed assembly shall be permitted to be cord connected if
a. The fixture is located directly below the outlet box or busway, and
b. The flexible cord is
1. Visible for its entire length outside the fixture,
2. Not subject to strain or physical damage, and
3. Terminated in a grounding-type attachment plug cap, busway plug or have a fixture assembly with a strain relief and canopy.


Joe Tedesco, NEC Consultant