#112230 04/29/01 10:10 PM
Joined: Oct 2000
Posts: 3,685
Likes: 4
Admin Offline OP
Administrator
Member
[Linked Image]
Submitted by Tom
Quote
Working clearance violation is the least of the problems here. Panel is shown as it was found. The ceiling tile is 10' above finished floor. What is hard to see is what appears to be a black cable at the bottom left corner of the panelboard. It is actually some #8 THHN with a heavy layer of tape that runs into the open end of a conduit just out of sight to the left. I'll leave it to others to spot the rest of the violations.

Tom

Horizontal Ad
#112231 05/01/01 08:48 PM
Joined: Oct 2000
Posts: 5,393
S
Member
man......

as many times as i see these things , it always sets you back stratchin' your head wondering who the guy with the brain tumor was.

is this in a convience store Tom ?

[Linked Image]

#112232 05/01/01 10:06 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Please don't tell me that this feeds the gas pumps!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#112233 05/01/01 10:39 PM
Joined: Oct 2000
Posts: 4,138
Likes: 4
Member
Looks like someone recycled a panel here (by the 2 in. ko's) Is that an FPE panel? Can't really make out too many details inside.

Bill


Bill
#112234 05/01/01 10:44 PM
Joined: Dec 2000
Posts: 4,294
Member
I don't suppose those holes in the top are for ventilation, being that you should get plenty of air by leaving the cover off like that. This is sick looking.

#112235 05/02/01 07:23 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Lovely, ain't it?

Actually, it is a Square D panel, it is recycled and is located in the social quarters (better known as a bar) of a fraternal organization.

I think we've picked on convenience stores enough for awhile. I wish I had pictures from the local fire department. Myself & 2 volunteer helpers straigtened it out a couple of years ago, I had 46 man hours in it & some of the work was so bad that the above picture looks good in comparison.

Bill, you really don't want to make out too many details on the inside. Typical 2 & 3 conductors in one terminal.

I've got a couple more working clearance pictures & I'll post them next week.

Tom


Few things are harder to put up with than the annoyance of a good example.
#112236 05/05/01 09:14 AM
Joined: Dec 2000
Posts: 84
C
Member
I'd like to focus on location of Panelboard. Are panelboards permitted to be located above a suspended ceiling?

Frank (cinkerf)

Horizontal Ad
#112237 05/05/01 11:21 AM
Joined: Oct 2000
Posts: 5,393
S
Member
oh oh, Frank wants us to think! [Linked Image] , good call !

ok, 384, nothing

240-24
hmmmmmm , what's the intent here ???? [Linked Image]

#112238 05/05/01 06:17 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Frank is on the right track. See 380-8(a) This is definitely too high.

240-24 is also a good call, see the definition of readily accessible.

110-12 for the unplugged holes, includes time clock on right.

Working space- the ceiling grid is in the way as is the wall that barely shows in the picture (left side), conduit that is between the panel & time clock, liquidtight flex on left side of panel. 110-26(a)(1), 110-26(a)(2),110-26(a)(3), a case can be made for 110-26(d) and 110-26(f)(1)(a). Whew.

As for the #8's & the tape job to the conduit, 300-10.

Had enuf?

Tom


Few things are harder to put up with than the annoyance of a good example.
#112239 05/05/01 06:48 PM
Joined: Oct 2000
Posts: 5,393
S
Member
uncle!

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Top Posters(30 Days)
BigB 4
Jam85 4
Popular Topics(Views)
328,009 Are you busy
252,860 Re: Forum
235,489 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5