ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 267 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#112091 03/03/01 05:13 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
<img border="0" src=&q...uot;300" height="307">

<font face="Arial" size="2" color="#FF0000">Click Photo for a closer look</font>


<img border="0" src=&q...uot;300" height="223">

<font face="Arial" size="2"><font color="#FF0000">Click Photo for a closer look</font>.</font>


<font face="Arial" size="2">Only standard locknuts and bushings were used
in 400 Amp. current transformer cabinet.
</font>


Frank Cinker

Pittsburgh, PA

#112092 03/03/01 05:52 PM
Joined: Oct 2000
Posts: 5,392
S
Member
OK Frank,
we have CT's, i see 4 wires, one possibly spliced thru. i see 208V colors, i think i see something green from the upper right of the box comming down.

I'm gonna go out on a limb here..

Are we dealing with a seperatly derived system, and violating 250-92?

[Linked Image]

#112093 03/03/01 06:17 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Shame on everyone involved. The installer failed to bond the cabinet & the conduit nipples (they might be bonded at the other end, though I tend to doubt it). If this passed inspection, the inspector was asleep & if it was energized by the power company, they too dropped the ball.

250-92 is clear about what is to be bonded & 250-94 tells you what you can/cannot use. Plain jane locknuts certainly don't cut the mustard & the #2 jumper from the grounded conductor to the CT cabinet is also missing. Also, the wireway in the upper right corner must also be bonded (bet it isn't).


Few things are harder to put up with than the annoyance of a good example.
#112094 03/03/01 08:36 PM
Joined: Dec 2000
Posts: 84
C
Member
Sparky,

Tom,

This installation has not been inspected yet. I took photo so I could present it to our City's Electrical Inspection Department. It's my job to review Contractor's work performed for our Department. I work for the City of Pittsburgh. The Contractor doesn't get paid if it is not a legal installation. It is clearly in violation of the section you mentioned Tom. It is a 120/208 Volt, Three Phase, Four Wire Service Lateral. The existing C.T. Cabinet was rusted. The Contractor installed a new one and reworked the raceway.

Frank (cinkerf)

#112095 03/04/01 10:05 AM
Joined: Dec 2000
Posts: 4,294
Member
They also might want to do something about that black neutral conductor.

#112096 03/05/01 03:10 AM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Is that a "Corner Grounded Delta Configuration" (tongue in cheek)?

Looks like a green tap on the A leg...

BTW...My wife is who spotted it!

I realize that these are supplied assembled, but is green the proper color for the CT tap?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#112097 03/05/01 07:18 AM
Joined: Dec 2000
Posts: 84
C
Member
Sparky,

Your wife has a good eye for noticing things. The green wire you see is a #8 AWG. One end attaches to the wireway in the upper right corner of photo. The other end attaches to a ground rod located beneath C.T. cabinet. I suppose that was an attempt to ground system.

Frank (cinkerf)