Burger to Go....and Please Hurry
#111571
01/06/07 07:41 AM
|
Joined: Dec 2000
Posts: 4,287
OP
Member
|
From HotLine1 It's a BK location; noticed the 'new' neon signage in the windows, and saw this while eating a quick lunch. John Arendt ![[Linked Image]](https://www.electrical-contractor.net/forum/el/hotline2.jpg)
|
|
|
Re: Burger to Go....and Please Hurry
#111572
01/06/07 11:05 AM
|
Joined: Feb 2004
Posts: 1,437
Member
|
I've seen 5-15 outlets that are made to snap into lighting track before... but I'm sure they cost more than the 59ยข cheaters. ![[Linked Image]](https://www.electrical-contractor.net/ubb/frown.gif)
|
|
|
Re: Burger to Go....and Please Hurry
#111573
01/06/07 03:34 PM
|
Joined: Mar 2005
Posts: 1,213
Member
|
Is that a 3-prong plug on 2-conductor zipcord? That makes about as much sense as the existance of plug adapters.
...actually, I'm trying hard to think of any actual codes this install broke! A (I assume) listed lamp base adapter was screwed in, and the plug adapter appears to be used correctly. And the only thing plugged in was a light. It might be skirting a requirement for a dedicated receptacle, and certainly not professional-looking, but is the installation actually unsafe?
[This message has been edited by SteveFehr (edited 01-06-2007).]
|
|
|
Re: Burger to Go....and Please Hurry
#111574
01/06/07 07:59 PM
|
Joined: Feb 2002
Posts: 183
Member
|
That looks like standard flat 3-conductor line cord. I would think you would want a good ground on that transformer; otherwise, the metal case (usually connected to the HV center tap) would likely float to a rather nasty voltage.
|
|
|
Re: Burger to Go....and Please Hurry
#111575
01/06/07 08:00 PM
|
Joined: Nov 2002
Posts: 790
Member
|
The ground pin doesn't connect to anything.
|
|
|
Re: Burger to Go....and Please Hurry
#111576
01/06/07 10:23 PM
|
Joined: Apr 2002
Posts: 7,235
Member
|
Major issue is the ungrounded neon transformers. There are numerous Article 600 violations in the neon HV wiring also.
The use of the adaptors, no matter how many, or what type, it's still no ground at the xfr.
Yes, there are receptacle units made by the track mfg, but how many sign guys might know that.
John
|
|
|
Re: Burger to Go....and Please Hurry
#111577
01/08/07 12:10 PM
|
Joined: Aug 2002
Posts: 1,691
Member
|
Well, at least they didn't snip the ground pins off the plugs. ![[Linked Image]](https://www.electrical-contractor.net/ubb/wink.gif)
|
|
|
Re: Burger to Go....and Please Hurry
#111578
01/08/07 05:11 PM
|
Joined: Nov 2001
Posts: 52
Junior Member
|
|
|
|
Re: Burger to Go....and Please Hurry
#111579
01/08/07 09:23 PM
|
Joined: Oct 2006
Posts: 745
Member
|
I find it hard to believe that a local inspector or fire marshal hasn't eaten there and might have brought it to the manager's attention.
---Ed---
"But the guy at Home Depot said it would work."
|
|
|
Re: Burger to Go....and Please Hurry
#111580
01/08/07 09:47 PM
|
Joined: Feb 2003
Posts: 288
Member
|
...actually, I'm trying hard to think of any actual codes this install broke!
210.50(B) 406.3(B) 410.47 600.3 (I'm sure the listing label addresses the grounding issue)
There are probably others. (2002 NEC)
|
|
|
|
|