Service in Garage #110973
08/14/06 10:41 PM
08/14/06 10:41 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,482
NY, USA
Quote
Some people just don't think ahead. The general contractors must be smoking something.

Alan Nadon
[Linked Image]

[Linked Image]

[Linked Image]

2017 / 2014 NEC & Related Books and Study Guides
Re: Service in Garage #110974
08/14/06 11:36 PM
08/14/06 11:36 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
It looks more like a carport, with no garage door. Still...


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Service in Garage #110975
08/15/06 04:34 PM
08/15/06 04:34 PM
C
Celtic  Offline
Member
Joined: Feb 2005
Posts: 361
NJ
Spontaneous Construction!


~~ CELTIC ~~
...-= NJ =-...
Re: Service in Garage #110976
08/15/06 07:08 PM
08/15/06 07:08 PM
C
Check Pilot  Offline
Member
Joined: Nov 2005
Posts: 141
Edmonton Alberta Canada
What kind of nutbar deal is this? Must be a real crowd pleaser when the meter readers come along. And what's with the cock-eyed light by the inside door? Roof too low or the light couldn't be moved down?

Re: Service in Garage #110977
08/16/06 07:53 PM
08/16/06 07:53 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
I got a few of these up here in 'Jersey'. Usually an un-permitted car port close-in. Interesting that the roof & siding show no signs of 'addition' work.

The leaning fixture was/is probably something that was on the 'Honeydo' list.

John


John
Re: Service in Garage #110978
08/17/06 06:14 AM
08/17/06 06:14 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
With the advent of remote readers, will accessibility of the meter be a non-issue in the future? (I mean with regards to locked doors and meter reading, not cramped closets and servicibility.)

I can certainly empathize with the homeowner here- they obviously didn't sink much money into that garage, and I doubt they could have afforded to move that meter. Then you get into other NEC issues regarding restriction on SE length and placement of the panel, and all of the sudden, the homeowner has $10k worth of electrical work for a $500 DIY job. Would be so easy to just ignore the problem, especially if you didn't even realize it WAS a problem. In fact, knowing how expensive the problem is, I'd probably have done the exact same thing...

Re: Service in Garage #110979
08/17/06 07:14 PM
08/17/06 07:14 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
Agreed, it's costly to relocate the service. but.......I'll play devils advocate.

Unprotected (service) conductors within the structure??

Also, how about the pressure vent gizmo on the gas meter??? Nothing like dumping into the structure!

Les: (LK) what do you say? ever seen one of these??

John


John
Re: Service in Garage #110980
08/17/06 08:15 PM
08/17/06 08:15 PM
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,431
Bakersfield, CA (Originally Or...
Seriously... how much would anyone charge to do that the right way??? Yank the old meter off the wall, 6X6X4 NEMA 1 pullcan, maybe 30' 1½" EMT and 40'X 3 #2THHN, and a meter/main breaker can (to eliminate the unfused feeder situation) landed on the side of the new garage a couple ground rods and 15' #6 AC and this would be good to go [Linked Image]Hell, you could probably salvage the old riser and feeders if they were really that hard up (I cant tell what condition they're in)
(This garage looks tiny, like Stuart Little might park there [Linked Image] )

PS. get the lazy phone guy to stop tying to our risers! [Linked Image]

Re: Service in Garage #110981
08/17/06 11:29 PM
08/17/06 11:29 PM
L
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
"Unprotected (service) conductors within the structure??"

Another one of those don't worry about the permit jobs, i bet the guy that did it, still thinks he knew what he's doing, the gas vent is good where it is, all the evidence will be gone, the first time the vent dumps!

That job will end up costing them, when they try to sell.

Re: Service in Garage #110982
08/18/06 07:31 PM
08/18/06 07:31 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
OK, I had 1 of these today. relocated to the left garage wall.

200 amp PSE&G pan; 200 amp rated service
2-1/2" RGC mast, boot, guy wire
200 amp CB main, 3R
40' SER to existing panel.
2 rods; jump water meter & water heater.
80' #4 to street side water main

Job Cost (on permit) $1675.00

John


[This message has been edited by HotLine1 (edited 11-16-2006).]


John
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,405 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.004s) Memory: 1.0259 MB (Peak: 1.2035 MB) Zlib enabled. Server Time: 2018-01-23 11:36:36 UTC