#110778 - 06/22/06 06:53 AM Water in UG Service  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,217
SI,New Zealand
Pics and info provided by e57:
Quote
Check existing service equipment at remodel. Looked around to actually find it... It was in a dog-house under an over-hang of the house, had to crotch to get to it. I open the dog-house door, and see a note to POCO, "Water comes out of meter, what should we do?" I think, well that a strange note? Lets open up and take a look.... I start at the main, which is above the meter.... Well what do you know, water in ther too, and an attempt to correct the problem by filling conduit with foam. I don't think I want to open the meter now.... Also notice that there is NO GEC at all, no rods, no water... and the main has two 2" KO's missing. I call this a "Just start over Service"


[Linked Image]


[Linked Image]


[Linked Image]

Thanks Mark!!. [Linked Image]


Let's face it, these days if you're not young, you're old - Red Green grin

2017 / 2014 NEC & Related Books and Study Guides

#110779 - 07/04/06 08:39 PM Re: Water in UG Service  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
I like the fancy cutout in the wood so the meter can fit through. That's cute. lol


#110780 - 07/05/06 01:48 PM Re: Water in UG Service  
RSmike  Offline
Member
Joined: Nov 2002
Posts: 134
Holland, MI USA
My uncle had a 'water powered' meter pan similar to this one. Water was running into his house and main panel. The breakers and entire panel were slowly rusting away. He was smart and called a sparky to have it fixed correctly. New panel and new entrance with proper fittings and weep holes to help prevent future issues.

So is the water just runoff from above getting into the open hole in the top or is there more fun stuff happening here. Obvious violation of Article 110.Stupid.12(A).
Are there any fastners holding this pan to the wall/board or is it standing on the conduit.

RSlater,
RSmike


#110781 - 07/05/06 09:00 PM Re: Water in UG Service  
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,431
Bakersfield, CA (Originally Or...
Sounds like a good place for an EYS seal off [Linked Image]

If its airtight enough for hazardous locations, it should be pretty water tight [Linked Image]



Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.003s) Memory: 0.7621 MB (Peak: 0.8928 MB) Zlib enabled. Server Time: 2017-08-23 12:01:58 UTC