ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left

Custom and Personalized Fall Gifts and Decor
Halloween Gifts and Decor

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,240 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#109842 12/19/05 10:25 PM
Joined: Dec 2000
Posts: 4,294
Member
Quote
These are pics of a service I came across out in the middle of nowhere on a house that had a service call..... The panel is 200A 120/240V, with #2 THWN feeders in a 1¼" riser, and it was approved by the AHJ! [Linked Image]

Randy (Lostazhell)

[Linked Image]


[Linked Image]


[Linked Image]




[This message has been edited by electure (edited 12-19-2005).]

Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

#109843 12/20/05 02:26 AM
Joined: Apr 2005
Posts: 200
H
Member
undersized conduit for the #2 THWN?


Cliff
#109844 12/20/05 11:03 AM
Joined: Feb 2004
Posts: 1,440
Member
Undersized conductors for a 200A service! [Linked Image] Minimum 3/0 THWN required for this size service.

#109845 12/20/05 02:13 PM
Joined: Oct 2004
Posts: 806
Member
Guys, to heck with the riser! [Linked Image]

How about the rat's nest of unsecured romex in that chase, the metal flex with romex in it that doesn't even connect to the panel.... [Linked Image]

I'd hate to see what's "under the hood" on this one!

Wonder what medication the AHJ was on too.... [Linked Image]


Stupid should be painful.
#109846 12/20/05 04:13 PM
Joined: Nov 2002
Posts: 793
Likes: 3
W
Member
That sticker looks to be several years old. The bad wiring probably happened after that inspection was done.

#109847 12/20/05 09:08 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I think the sticker is left over from the house it was previously installed in, somewhere else.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#109848 12/20/05 10:55 PM
Joined: Feb 2005
Posts: 361
C
Member
Quote
Originally posted by Lostazhell:

Undersized conductors for a 200A service! Minimum 3/0 THWN required for this size service.

...and for that area?
See:Table 310.15(B)(6) (2002)


That is quite a mess!


[This message has been edited by Celtic (edited 12-20-2005).]


~~ CELTIC ~~
...-= NJ =-...
Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

#109849 12/21/05 09:32 AM
Joined: Nov 2001
Posts: 745
M
Member
What a quality installation!! It looks like somebody beat this thing into the wall with a sledgehammer.

A couple of questions, Randy: What's up with the black romex'es (tied in a knot)? and, what was the nature of your service call there (at this house...?)?

This thing is quite literally a "Pandora's Box".

Mike (mamills)

#109850 12/23/05 10:42 AM
Joined: Feb 2003
Posts: 687
A
Member
We can't suport a drop around here with 1 1/4 RMC even if it is a 100 A service.

They want 3" RMC for 200 amp if the mast is supporting the drop.

Is this CA where the mast is on the inside wall? We allways go on the outside with the mast.

Tom

#109851 12/23/05 01:36 PM
Joined: Jul 2002
Posts: 8,450
Likes: 4
Member
Just a little comment Randy.
I like the idea of that rain water deflector on the mast.

Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5