#109656 11/17/05 10:33 PM
Joined: Dec 2000
Posts: 4,293
Member
One of the guys was unscrewing a blank cover on a different box about 100' away when he heard the pop inside the box he was working on. The screw had apparently rubbed a conductor raw inside.

The simultaneous sound of this one kind of made it hard to hear, though.




[Linked Image]


[Linked Image]

Horizontal Ad
#109657 11/17/05 10:52 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Just a guess that one of the switches was not happy with the available fault current.

That is really ugly.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#109658 11/17/05 11:22 PM
Joined: Jul 2002
Posts: 8,441
Likes: 4
Member
Scott,
What make/brand switches are those?.

#109659 11/17/05 11:54 PM
Joined: Feb 2003
Posts: 939
F
Member
i am sure it look like Hubbel 2 pole switch but the Pass & Syemour look very simuir too but i am not too sure about Levetion they look little diffrent

i can tell this was wired up on 277/480 volt circuit

if running more than 300 volts it should have " divider " on there and i dont see any of it in the switch box at all.

the other thing i can see that the switch is allready wired on 480 volts [Linked Image] so that get more spooky there

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

#109660 11/18/05 01:15 AM
Joined: Feb 2004
Posts: 1,440
Member
Were these 4ways or 2pole switches? If they're 2 pole, and there was 480V being run through these, the fault downstream (I'm assuming) probably found its weakest link being the switch contacts not being rated for the fault voltage.. But you say a faceplate screw caused the fault which would be at 277V if all was grounded properly, or did more than one wire get damaged?

The switches are Hubbell, you can make out their oval insignia above the toggles on the yokes...

#109661 11/18/05 08:26 AM
Joined: Dec 2000
Posts: 4,293
Member
Yup, Marc's right. (I told the answer on the chat, which may have helped [Linked Image])
2 Poles, Hubbell, with a label on the side "2 Pole for single circuit only".

The installer chose to disregard the label, and ran 480V through them. The fault was 277V, caused by 8-32 in the corner of a 4-S box. The switch on the left took the fault, and its failure sent this "Jack and the Beanstalk" effect into high gear.

There were 18 of these switches installed (that's 36 circuits). The customer had me remove all of them [Linked Image]
They will be replaced with contactors.
(BTW, None of the 20 Amp breakers tripped)



[This message has been edited by electure (edited 11-18-2005).]

#109662 02/02/07 08:02 PM
Joined: Dec 2000
Posts: 4,293
Member
[Linked Image]

Here's what I found instead of contactors when I happened by the place again.


[Linked Image]


Now what ??

[This message has been edited by electure (edited 02-02-2007).]

Horizontal Ad
#109663 02/02/07 08:33 PM
Joined: Apr 2004
Posts: 812
Member
Where's that rolleyes smiley, wait, here it is! [Linked Image]

Whaddaya expect? Someone to spend money replacing the old switches with new contactors?

(BTW Scott, no cursing. [Linked Image] )

Ian A.

[This message has been edited by Theelectrikid (edited 02-02-2007).]


Is there anyone on board who knows how to fly a plane?
#109664 02/03/07 07:48 AM
Joined: Aug 2001
Posts: 7,520
P
Member
To quote a character from an old British movie about a couple fixing up an old house (including wiring):

"They never learn!"

#109665 02/03/07 11:16 AM
Joined: Feb 2004
Posts: 1,440
Member
I wonder if this is why the code wants dividers for >300V.. to block the shrapnel from the other switches. [Linked Image]

I have an old GE 3P toggle switch rated 20A 600V if they're really against the contactors, they might want to look into them. I'm sure they're not cheap though. Here are the ones from P&S..

edited to fix link

[This message has been edited by Lostazhell (edited 02-03-2007).]

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Top Posters(30 Days)
Admin 3
CSS 1
Popular Topics(Views)
365,209 Are you busy
288,084 Re: Forum
266,766 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5