Completion tests #10943
06/23/02 05:54 PM
06/23/02 05:54 PM
P
pauluk  Offline OP
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
I don't recall this being discussed before.

Does the NEC specify what tests must be carried out upon completion of a new installation? Or is there a generally accepted series of tests that are performed?

I'm assuming that you would as a minimum do a megger test on the final system, but what about ground rod testing, verification of correct polarity, and so on?

Work Gear for Electricians and the Trades
Re: Completion tests #10944
06/23/02 06:38 PM
06/23/02 06:38 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Paul,in addition to checking overall installation and compliance to other ares of the code, most inspectors will check polarity with a receptacle analizer, check grounding with an ohmmeter, and require Fire alarm certification at the final inspection.

Most insulation and ground test are specified in the engineers specifications, although I have had inspectors who requested ground readings at the GEC. (ground megger)

The kicker to this is, per the NEC, if you can not achieve a value of 25 ohms or less on a ground rod you must add a second rod and that is all that is required whether this gets the 25 ohm minimum or not.


In medical installations certifications of equalpotential grounding, Isolation systems commissioning, Fire alarm certification, Generator commissionig, Critical, and Life safety branches to name a few are required.

This in the areas I work, some others may have other standards.

Roger

Re: Completion tests #10945
06/23/02 07:47 PM
06/23/02 07:47 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,349
Paul, this is all i've found......

Art 550, Mobile Homes, Manufactured Homes, and Mobile Home Parks.
550.17 Testing.

(A) Dielectric Strength Test. The wiring of each mobile home shall be subjected to a 1-minute, 900-volt, dielectric strength test (with all switches closed) between live parts (including neutral) and the mobile home ground. Alternatively, the test shall be permitted to be performed at 1080 volts for 1 second. This test shall be performed after branch circuits are complete and after luminaires (fixtures) or appliances are installed.

Exception: Listed luminaires (fixtures) or appliances shall not be required to withstand the dielectric strength test.


(B) Continuity and Operational Tests and Polarity Checks. Each mobile home shall be subjected to all of the following:
(1) An electrical continuity test to ensure that all exposed electrically conductive parts are properly bonded
(2) An electrical operational test to demonstrate that all equipment, except water heaters and electric furnaces, is connected and in working order
(3) Electrical polarity checks of permanently wired equipment and receptacle outlets to determine that connections have been properly made

Re: Completion tests #10946
06/24/02 01:21 PM
06/24/02 01:21 PM
P
pauluk  Offline OP
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Thanks.

Our "regs." specify tests for correct polarity at outlets, switches in "hot" conductor, ground continuity, and so on.

Interesting on the mobile-home megger tests. For 1-ph 240V and 3-ph 240/415V our standard insulation test is at 500V DC (between every possible combination of phases & neutral, and between all phases+neutral strapped together and ground).
Absolute minimum allowable result is 0.5 Meg, although the IEE recommends that anything under 1 Meg be investigated further.

I should have also mentioned several tests specific to our ring circuits (Uh-oh! Not those again!).


[This message has been edited by pauluk (edited 06-24-2002).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,849 Are you busy
184,205 Re: Forum
173,446 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9603 MB (Peak: 1.0916 MB) Zlib enabled. Server Time: 2018-05-21 08:53:23 UTC