Is this mast service properly supported? Shouldn't there be additional support? (230.28?)
-richard
|
|
|
|
|
Joined: Dec 2000
Posts: 4,293
Member
|
I think the term "adequate strength" is subject to interpretation. Another item in 230.28, though, is not. "Only power service-drop conductors shall be permitted to be attached to a service mast." The phone and cable TV(?) wires have got to go...S
|
|
|
|
|
Joined: Feb 2003
Posts: 67
Member
|
poco in this area requires a guy or brace when mast exceeds 3' over roof.it also considers the length of the conductors and any strain on the mast.
|
|
|
|
|
Joined: Oct 2000
Posts: 4,158 Likes: 5
Member
|
Our POCO requires a minimum of 32" between supports and if mast extends more than 5 feet above last support it must be 3-1/2" Galv pipe.
Bill
Bill
|
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Are those one-hole straps that are securing it to the building?
|
|
|
|
|
Joined: Oct 2000
Posts: 3,672 Likes: 4
OP
Administrator Member
|
I took closer look and found the clamps to be bolted . the last clamp is 16 inches from the roof, and the 10 foot mast is 5 feet from the top of the meter to the top of the roof. -richard
|
|
|