#107737 08/02/04 09:53 PM
Joined: Oct 2000
Posts: 3,685
Likes: 4
Admin Offline OP
Administrator
Member
Quote
Found this service with the neutral and phase conductors reversed in the meter base while performing a final inspection on a single family dwelling.

- necbuff
[Linked Image]

[Linked Image]

Horizontal Ad
#107738 08/03/04 12:39 AM
Joined: Feb 2004
Posts: 1,438
Member
Aside from the darwin award for not even being able to wire a meter socket, Please tell me thats not a bare AL ground wire going right in front of the main lugs for the panel?!?!?!? [Linked Image]

-Randy

[This message has been edited by Lostazhell (edited 08-03-2004).]

#107739 08/03/04 01:05 AM
Joined: Jul 2003
Posts: 394
B
Member
I think most 3 year-olds can match colors better than that. Things we do totally without concious thought are far beyond some people.

#107740 08/03/04 02:05 AM
Joined: Sep 2002
Posts: 946
Likes: 2
N
Member
Good panel, sloppy "work".

#107741 08/03/04 02:16 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Is this service live?!!!!

No ground or bond between the meter and main, so the main case and neutral is 120, and one phase 0, the other 220?

Looks like some smoke damage there on the riser neutral?

This may not have happened if this person hadn't gone through all the "red tape" getting it inspected. Nice catch, and a real good thing you looked!


Mark Heller
"Well - I oughta....." -Jackie Gleason
#107742 08/03/04 12:41 PM
Joined: Nov 2003
Posts: 269
E
Member
The GEC in pipe is nice although I dont understand the gap between end of pipe and meter can.


John
#107743 08/03/04 08:59 PM
Joined: Jul 2004
Posts: 41
N
Member
Service not energized, I am AHJ and I obviously rejected this one. That is an insulated conductor in front of the lugs and the reason for the gap is for other utilites to have a spot to hit the GEC for their service, eg; catv, phone.


Kenny Wilee
Horizontal Ad

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Popular Topics(Views)
340,263 Are you busy
265,660 Re: Forum
246,668 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5